Can we loop AC neutral wire with DC neutral wire?
Answers were Sorted based on User's Feedback
Answer / raj
No.we cannot loop ac,dc neutral.because in unbalance condition some current flow with the neutral.ac and dc current shouldn't be mixed
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / s.r.nalawade
1.In AC circuit there is 'NEUTRAL' point where as in DC circuit the negative terminal is always connected to battery negative.
2. Consider example of Diesel generator. Battery is used for giving start command to starter motor through solenoid. Same battery is used for configuration of RUN/STOP command. Digital switching inputs like low oil pressure, high coolant temperature, remote start/stop are active low. i.e when battery negative is activated, generator controller will respond immediately.
3. Also there is main AC alternator coupled with engine. L1,L2,L3 & neutral are four terminals from alternator.
4. If AC neutral & DC negative is kept common, then unbalance neutral current will interfere with DC negative. Also, you will get line to neutral voltage (240V AC in case 3 phase 415V, 50 Hz system). Imagine the adverse effect of such a high potential on controller digital inputs. Also, as engine block, mounting skid & alternator body & battery negative terminal is interlinked, it will cause electrical shock to operator in contact with generator. Therefore AC neutral must be isolated from DC negative.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / maddy
No, you cannot loop AC neutral wire with DC neutral wire.
Since AC current flows in both directions (forward and reverse), looping the AC with DC will make AC flow in the DC circuit. You dont want that to happen for a lot of reasons.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / makku
I don't believe this is up to code, but it will pass the test from a standard outlet tester. The problem I see is if any device plugged into the outlet comes into contact with a ground (e.g. water) and that path is more efficient than going all the way back on the neutral wire through the house wiring, then hot current going through any appliance and onto the neutral would come out the ground and possibly electrocute anyone in that path.
| Is This Answer Correct ? | 0 Yes | 0 No |
how the diesel generator maintain the rpm when the generator loaded varies from 10% to 70% immediately?
why it is so called as xlpe(cross linked poly ethyline) cable?
If we have 11 kv RYB Phase single core cable near about. Then wht effect and losses
Why used in layer by layer charcoal and salt used in earth pits.
11 Answers CESC, HP,
Transfer function is == ? a. Mathematical model b. System with no physical structure c. Can be calculated through differential equations
dear sir, i completed diploma in electrical in 2005, how i can get electrical supervisor liance in mumbai
what is the acceptable insulation resistance for motor/transformer?
2 Answers Reliance, Tata Motors,
When we change the tap position of 10MVA transformer it suddenly tripped with Out of step indication and also with Static differential relay indication, Transformer Bucholz relay indn and Low oil level indication. Before 1 week the same problem occured by changing the tap position. but at that time only oltc bucholz relay activated. After testing the TxR Relay team & PET team cant find any solid reason. The values are ok also. So plz answer wat's the reason for this incident? anybody plz help.
what is the purpose of battery tap voltage.
3 Answers ABB, Crompton Greaves,
How one may guess the direction from which the distribution line is incoming if there is no pole plate on poles?
We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11KV switch yard having 12.5MVA power transformer. Some times we draw power during emergency. It is observed that during Export or Import for load less than 500Kw the power factor is decreasing to 0.3 . This is happening only during export or import. During island condition TG power factor OK.Our capacitor bank is provided with our Power plant auxilliary load. Please suggest how I can we improve our power factor during low load (GRID).
In Transformer testing at Shop test we normally test for vector group, open ckt.,short ckt. but what are the other test performed for transformer once it reaches at site.For e.g:if the transformer is dry having rating 1000KVA?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)