Can we loop AC neutral wire with DC neutral wire?
Answers were Sorted based on User's Feedback
Answer / raj
No.we cannot loop ac,dc neutral.because in unbalance condition some current flow with the neutral.ac and dc current shouldn't be mixed
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / s.r.nalawade
1.In AC circuit there is 'NEUTRAL' point where as in DC circuit the negative terminal is always connected to battery negative.
2. Consider example of Diesel generator. Battery is used for giving start command to starter motor through solenoid. Same battery is used for configuration of RUN/STOP command. Digital switching inputs like low oil pressure, high coolant temperature, remote start/stop are active low. i.e when battery negative is activated, generator controller will respond immediately.
3. Also there is main AC alternator coupled with engine. L1,L2,L3 & neutral are four terminals from alternator.
4. If AC neutral & DC negative is kept common, then unbalance neutral current will interfere with DC negative. Also, you will get line to neutral voltage (240V AC in case 3 phase 415V, 50 Hz system). Imagine the adverse effect of such a high potential on controller digital inputs. Also, as engine block, mounting skid & alternator body & battery negative terminal is interlinked, it will cause electrical shock to operator in contact with generator. Therefore AC neutral must be isolated from DC negative.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / maddy
No, you cannot loop AC neutral wire with DC neutral wire.
Since AC current flows in both directions (forward and reverse), looping the AC with DC will make AC flow in the DC circuit. You dont want that to happen for a lot of reasons.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / makku
I don't believe this is up to code, but it will pass the test from a standard outlet tester. The problem I see is if any device plugged into the outlet comes into contact with a ground (e.g. water) and that path is more efficient than going all the way back on the neutral wire through the house wiring, then hot current going through any appliance and onto the neutral would come out the ground and possibly electrocute anyone in that path.
Is This Answer Correct ? | 0 Yes | 0 No |
if we want to increase the back up time of an UPS what should we do ? if we want to decrease the charging time of a battery/batteries attached with the UPS what should we do ?
What happen if a 18 watt fluorescent tube is used on 36watt choke,which one damaged or not damaged, if damaged why that damaged?
the winding of Gen and Motor is star or in delta ??? and why
mention hazard experienced during installation
I have 4 busbar of 1000 ampere. we use 4 busbar to make 4000 ampere in one phase.my problem is that when we applied 60% load on that then busbar produced high noise.what is the reason of that and how can i minimize that noise.
0 Answers College School Exams Tests,
sir please tel me how calucalte kwh if home taken load 30ams how maney kwh taken per day.and 3phase motor 5hp per hars how maney load teken and how mach kwh and forward me to electrical table for calicalte kwh and kvr and kvah
Sate maximum power transfer theorem?
When the power Factor (p.f)is lead then how the Voltage can rises?
why motor rating in kw?
Under Ground Power cable earthing is required at both end or single end? and reason for the same
When steam condenses and becomes water at the same temperature, the specific heat for the process in kJ/kg k is
List the materials required for Pipe Earthing.