Why Closing coli supervision is not required for Circuit
breaker.
Answer / seshu
In the protection philosophy our aim is to protect the system under abnormal conditions for which we require tripping of the circuit breaker. So that every circuit breaker having 2 nos Trip coils (for redundancy).Once the breaker closed it has to trip so the monitoring of Trip coil supervision is necessary .In general closing coil supervision is not necessary and it would be additional cost
Is This Answer Correct ? | 7 Yes | 0 No |
What will happen if the interpoles in case of a generator have opposite polarities to that behind it in the direction of rotation ?
if name plate detals of a motor or any other is missing then how to find it
If I have a motor of 1 MW with 6.6 kV, running at 35% load, how can I save energy without reducing the load?
why an ac solenoid valve attract the plunger eventhough we interchanges the terminal?will the ploes changes?
is that any software calculator to calculate the size of cable
what is conductor constant taken for calculation of voltage regulation of 11 kv and 33kv line on dog aor rabbit conductor
1 Answers CSPDCL-Chhattisgarh State Power Distribution Company Limited,
Why in 6 KV XLPE cable termination kit used and why not in 380 V xlpe cable same is not used
What is quadrantal symmetry?
Wat is da difference b/w neutral earthing and unearthed system?
Describe the test procedure to determine the vector group
which is more danjerous high voltage or high current
what is closing resistor in circuit breaker? why it used?