Diff between Earthed & Unearthed cable ?
Answer / mds.1490@gmail.com
n 3phase earthed system, phase to earth voltage is 1.732
times less than phase to phase
voltage. Therefore voltage stress on cable to armor is 1.732
times less than voltage stress
between conductor to conductor. Whereas in unearthed system,
(if system neutral is not
grounded) phase to ground voltage can be equal to phase to
phase voltage. In such case the
insulation level of conductor to armor should be equal to
insulation level of conductor to
conductor.
For example for a 6.6kV ungrounded system, 6.6kV/6.6kV (UE)
class cable has to be used while 6.6kV/3.8kV (E) class
cables are adequate for solidly earthed systems. The
UE-class cable is
naturally costlier than the earthed class of cable.
Is This Answer Correct ? | 2 Yes | 0 No |
what is the purpose of reactor in electrical substations ?
Define cut-off rate?
why do some transmission towers have two insulators at one side and three insulators at the other side
Why we use 4-20 mA Analog signal for the PLC input? Why not 0-20 mA? Why not 5-25 mA?
What are the advantages and disadvantages of short-pitched winding?
A 3-phase IM is supplied from 50 Hz system. It runs at speed of 1440 rpm and slip equal to 4 %. Calculate rotor frequency. A 50 Hz B 0 Hz C 4 Hz D 6 Hz
Why the underground cables will Punchar? or what is the reason to burst the underground cables?
After synchronization with grid how to maintain the power factor in lagging or in leading? if lead of lag what is the problem?
what is the difference between megger and earth tester?
28 Answers Ashok Leyland, IOCL, RRL,
What are two contours of nichols chart?
What is the Difference Between the SCADA & PLC ? Both it also control and Supervise Then what Special in Scada & PLC?
i m doing DEEE in part time,can i join regular cources in BE,,IF i join what the cources can i select like (civil,ece,IT) ,,kindly advice