If the system is three-phase: KVAR=sqrt(3)*Icap[A]
*Volt/1000 then:
Icap=1000*kVAR/Volt/sqrt(3)
If the ambient temperature will remain the same and if
permissible conductor temperature will be the same then
copper bus bar cross section required will be 70%[approx.]
from Aluminum bus bar.
| Is This Answer Correct ? | 2 Yes | 0 No |
What is the difference between CT for protection and Ct for metering?
Difference between Profibus DP/PA?what does it stand for and how is it use in process?
What will happen if 33 kv is given to a 11/0.415 kv Distribution transformer?
Define transfer function?
what is the function of breather in a transformer
29 Answers Areva, Bhel, RKM Powergen, Vijai Electricals,
Is it required to use 2 nos of body earthings to any machine though if we use TP with E supply is provided to Machine?
9.The material used for coating the electrode is called........
how to calculate busbar size? if ex:1000amps i need to calculate busbar size and what size of bar?if any example caculation pls give the formulas.
Wind mill
what is the procedure for erection of a transformer
How to calculate wire length,size & current? ( related to control panel)
0 Answers FSS, GK Controls, Panel Tech,
IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoing breaker kA rating to be equal to busbar kA rating?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)