Why transformer rating in KVA? describe.
Answers were Sorted based on User's Feedback
Answer / shiva
kva is active power+ reactive power
the really used power is active power only.
which is v*i*cos pi.
but we dont know user's power factor so ratings are kva for t/f.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / biswaranjan das
Transformers Are Rated In Kva Because Generally There Are Two Losses In A Transformer I.e Core/iron Loss & copper Loss Due To Transformer Is A Stready Device So Their Is No Loss Of Mechanical . Due To the Core Losses Depends upon Voltage(v) & copper Losses Depends Upon Current(A) So The total Losses Depends Upon VA I.e KVA .
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / sandip paul
Trafo losses depends on voltage and current only. voltage
influences the core loss or no load loss and current or
load influences the copper loss. no loss depends on power
factor of the load. thus efficiency is mainly governed by v
and I only. hence o/p whis is the ratio of (i/p - losses)/
i/p is controlled by v and I. Hence trafo rating is defined
in KVA no KW.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / rams
due to the losses of transformer dependas on the current
and voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
transformer rating in
kva because power
factor of transformer
is always depended on
other load.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is work of CTPT in 33/11kv Substation
Specify the crystal frequency required for an 8085 system to operate at 1.1MHz
200-100/1-1A – Transformer Knee point voltage
What is C2-M2-E2 class in circuit breaker. why and where it is to be used in circuit breaker
how to calculate the starting current of a motor? gopal
What are the difference between normal application Transformer and Solar application Transformer?
how can the active power and reactive power of an alternator be controlled?
What is the standard height of installation of Socket & switch from Finish Floor Level as per the IEC/IS Rules?
what is elcb
To transmit the Power which must be present…? a) Reactance b) Resistance c) Capacitance d) none of above
What is the purpose of stand by earth fault protection for transformer ?
How to calculate the Short Circuit Impedance in Transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)