Answer / ezhil
the full load amps of 500kva transformer is
kvax1000 / 1.732 x v
500x1000 / 1.732x415
500000/719 = 695A
Hence we can select 2R X 3C X 300SQMM
Is This Answer Correct ? | 15 Yes | 3 No |
Answer / satyendra kumar
find the total load whatever rating of trnsformer---------------i=kvax1000/secondary voltage. we find total load then select of cable size i think 500sq2mm
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / dharmendra
post your full question input cable or output cable
you can use V1xI1=V2XI2
Is This Answer Correct ? | 6 Yes | 11 No |
what is ICU and ICS in breaker ratings
what is distribution board?
figure of phasor diagram of transformer when full load or no load ?
How to do maintenance of transformer feeder.
The screw thread commonly used for transmission of motion is one of the following types of threads
differtiate between energy consevation and energy efficiency..
what is the most permissible winding temp when we conducting a generator load test?(condition no load)
How to detect voltage vector shifting in interconnection protection.
How we calculate the Multiplying Factor of Kwh meter for 3 phase alternator.
in our transmisison sub station why we step down firstly 132kv\33kv then 33kv to 11kv. can we direct step down 132kv to 11kv.
What is rated value? is it phase values or line values?
In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours, what would be result of this condition?