Answer / ezhil
the full load amps of 500kva transformer is
kvax1000 / 1.732 x v
500x1000 / 1.732x415
500000/719 = 695A
Hence we can select 2R X 3C X 300SQMM
| Is This Answer Correct ? | 16 Yes | 3 No |
Answer / satyendra kumar
find the total load whatever rating of trnsformer---------------i=kvax1000/secondary voltage. we find total load then select of cable size i think 500sq2mm
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / dharmendra
post your full question input cable or output cable
you can use V1xI1=V2XI2
| Is This Answer Correct ? | 6 Yes | 11 No |
We store the d.c supply...then why can't we store A.c supply???
Define transfer function?
Why delta star trformers are used for lighting loads?
what is the rating of a power transformer?
Meaning of CTPT ,how it works &how it measures the reading on trivecter meter,&what is trivecter meter
1 Answers PF, Student, TSSPDCL,
why most of junction box vendors providing T5/T6 Temp class jb's for T3 area any special reason?
iam interesting to design the control panel for 3 phase pump motors by controling single phase switches.iam plan to use fuse,contactor & relay for motor protection .how can i select the voltage & amps rating for fuse,contactor & relay plz guide me .if anybody clarify my doubt means it will more helpful for my future .
1.what is the difference between transformer differential and busbar differential.2)why we are using 2 slope for trafo diif and 1 slope for busbar diff.3)what is the purpose of metrosil and stabilizing resistor in high impedance relay circuit.4)how metrosil reduce the peak volage.5)what is the funtion of stabilizing resistor
I WANT TO INSTALL LIGHTING ARRESTOR ABOVE 20 FEET HEIGHT INDUSTRIAL BUILDING. NOW IT WAS 15 FEET HEIGHT HOW MUCH DISTANCE IT WILL COVER & HOW TO CALCULAT THE DISTANCE COVER BY THE ARRESTOR
A three phase transformer 460v primary 220v secondary (three phase four wire system.) Why did we get 460 volts across the neutral on the secondary side?
A.V.R maintains the voltage of a generator when it is in island mode but when the generator is synchronised with grid it maintenance the P.F,how it happens please any body explain it in detail.
what happens if we connect two parallel ideal voltage sources across resistor?what is current flowing through resistor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)