Answer / subbarayalu
The normal method
of expressing transformer impedance is as a percentage voltage drop in the
transformer at full-load current and this reflects the way in which it is seen by
system designers. For example, an impedance of 10% means that the voltage
drop at full-load current is 10% of the open-circuit voltage, or, alternatively,
neglecting any other impedance in the system, at 10 times full-load current, the
voltage drop in the transformer is equal to the total system voltage.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / anonymous
It is because three phase system is most economical out of all possible polyphase system configurations...that's it...
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sokib
why did electric polyphase system commonly using three phase
system? is there any electrical system more than three phase
system?
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / 7anoter4
Usually group of transformers presents the same short-
circuit reactance in %
For instance, for S[ rated power] up to 2500 [to 3000] kVA
the percent reactance will be vk%=4-8. Ohmically calculated
reactance will be V^2/S*vk%/100 [ V=rated voltage].
For V=10 kV and vk%=6 for S=500 kVA Xk=10^2/0.5*6/100=12
ohm
For V=6 kV and vk%=6 for S=3000 kVA Xk=6^2/3*6/100=0.72 ohm
As one could see it is more convenient to consider only
vk% instead of ohmic reactance
| Is This Answer Correct ? | 0 Yes | 1 No |
What is harmonics in AC waves. How it is generated? How it will effect the system network? how can eliminate it?
Define damping ratio.
long form of CT
3 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
What are PLC leader logic program method
what is positive , negative & zero equivalent system resistance
How much pf maintan in dg set in 6o% load,when Dg runnig Neutaal Earthing removed what happen.
how can we select the rating of Load break switch that is connected to the primary protection of 200 kva 11kv/415v distribution transformer?? step by step calculated answr pls...thnk.u
How do performance buccholz relay testing in power transformer
Am i eligible to get electrical supervisor licence? As i did diploma as well as degree in Electrical Engg. in June 2011. Now i am working in 15 MW Power plant from 2 mnths. i belongs to Maharashtra.
What is difference between 220v/50Hz & 120V/60Hz?
can I connect 25KvA stepdown transformer(RYB-440V,UVW-240V) to the output of 15KvA,3-phase online UPS(440V phase to phase)please brief.
What are the reason of unbalanced secondary voltage of HT transformer 33kv/6.6kv ? Incomming voltage is balanced.33kv each secondary voltage 6.6 kv 6.4 kv 6.4 kv At no load conditions.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)