Consider a control valve action,the inlet air pressure is only 6 ksc but
physically how it can be operate against 100 ksc line fluid pressure?
Answers were Sorted based on User's Feedback
Answer / ys
actally pressure=force/area.. here ctrl valve operates
against a very small area(the plug seat area).so the force
required for this also less. hence the ctrl valve acts
against high pressure
| Is This Answer Correct ? | 7 Yes | 2 No |
The reference to 6 ksc pressure means that the valve uses a
pneumatic actuator.
The ability of a pneumatic actuator to work against the line
pressure depends on the force that it can exert on the
valve's plug/cage/trim against the line pressure's force and
the bench setting of the spring.
A maximum of 6ksc of air inlet pressure can be exerted on
the total area of the actuator's diaphragm.
If the diaphragm area * air inlet pressure > plug area *
line pressure force + spring force, then the actuator will
move the valve plug. If not, the line pressure will move
the actuator.
A standard step in sizing a valve assembly with an actuator
is to check that the actuator can close against the maximum
line pressure and the spring setting at a given air supply
pressure. All vendors provide sizing charts for this purpose.
| Is This Answer Correct ? | 2 Yes | 0 No |
What is possitive and negative feedback?
sir,would you please send me the Hindustan petroleum corporation limited papers(HPCL).my e-mail ID is ujjwal_sharma1983@yahoo.com
how to calibrate a capillary type level transmitter for a closed tank in field? also what is the procedure for commissioning a capillary level transmitter for a closed tank?
what is difference between E/P positioner and I/P positioner. Why E/P fixed in below actuator and why I/P fixed in other place
Why we use 250 ohm resistor in series with HART protocol communication?
13 Answers Chemtrols, Instec, Sabic,
TCD Principle
how to calibrate TT transmitter
What are the type of bonnets in the control valves?
What is the use of +/- 20ma in analog measurement,and which instrument gives +/-20ma output
Displace type LT to be calibrated in workshop, wt. 40, dia- 60 mm, density- 0.8kg/cm3.
we have level transmitter for h2s04 storage tank capacity 10k ,always there are failure of transmitter due to failure of magnetic floats ,please come up with solutions at the earliest.
For what reason would you possibly be compelled to make use of a Smith Predictor. Explain the idea behind the operation of this device.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)