what is the meaning write of AC1,AC2,AC3 .....power contactor
Answers were Sorted based on User's Feedback
Answer / pani
Relay types
Ac1-Noninductive loads (pf 0.95).
Ac2-Slip Ring Induction Motor.
Ac3-Squirrel Cage Induction Motor.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / muttappa
AC1,is for resistive load and
AC2, is special conditions of motor
AC3,is for normal motor loads
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / nitin tyagi
AC-1 - This category applies to all AC loads where the power factor is more than 0.95. These are primarily non-inductive or slightly inductive loads, such as heating. Breaking the arc remains easy with minimal arcing and contact wear.
AC-3 - This category applies to squirrel cage motors with breaking during normal running of the motor.
On closing, the contactor makes the inrush current, which is about 5 to 7 times the rated full load current of the motor.
On opening, the contactor breaks the rated full load current of the motor.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / abdul rehman khalid
This applies to all AC devices (loads) with a power factor of at least 0.95 (cos phi greater than or equal to 0.95).
Example of use: resistive load, heating, distribution.
This applies to squirrel cage motors where breaking occurs while the motor is running.
Example of use: all squirrel cage motors, lifts, escalators, conveyors, bucket elevators, compressors, pumps, mixers, air conditioning units, etc.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / abdul rehman khalid
AC1..This applies to all AC devices (loads) with a power factor of at least 0.95 (cos phi greater than or equal to 0.95).
Example of use: resistive load, heating, distribution.
AC2..This applies to squirrel cage motors where breaking occurs while the motor is running.
Example of use: all squirrel cage motors, lifts, escalators, conveyors, bucket elevators, compressors, pumps, mixers, air conditioning units, etc.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / vimal dobal
AC1, AC2, AC3..are like a normally auxallery contector. Use
to indirect operation of High reated power contractor.
| Is This Answer Correct ? | 7 Yes | 30 No |
is there any device that works properly accept relay, it may be fuse but if i want fuse of 33kv 300 amp it is avaliable, pls give me details
what is power factor?
surge tank, hrc fuse, earthing transformer, firm power objective type
How to select the rating of the Transformer?
how to calculate size of cable from motor current given and how to calculate full load current of a induction motor.
what should be the no load current for 3 phase ac motors ranging from 5 kw to 1000kw?
hi all i like to know vat is power plot in control systems also i want to know abt latest trends in electrical & electronics
1)How much current can a 3-1/2 core 100 mm wire carry? 2)What are the special cables required for explosion proof wiring? 3)In case you do not have coal and salt for earthing, how can you achieve good temporary earthing? 4)One horse power single phase motor is more likely to get hot than a one horse power 3 phase motor. Is it true or false, if true why? 5)What are the different types of soft starters for large motors?please explain?
what happens when current(ac or dc)flowing through a boucket of water?please describe it.
What is disc insulator and it's application..?
How to calculate incomer of a capacitor bank/feeder from its KVAR, AND how to calculate the copper busbar for rated incomer,like for 400A we calculate the 40x10 of aluminum busbar.
Why r u using pf panel. what the uses
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)