If the Barrier Fails during online then What will be the
control valve position in field or Positioner action in the
field.
Answers were Sorted based on User's Feedback
Control valve will turn its failure position either close or
open (FO/ FC)
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / nikunj dungarshi furia
it will return to its position at no signal condition i.e.
either normally closed (air to open / fail closed) or
normally open (air to close / fail open)
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / james
Based on the process
1st If barrier fails before escalating to a incident - The answer is fail safe c/v CLOSE
2nd when barrier fails - fail safe action done - Then the fail safe action will be - c/v OPEN to atm / flair
Is This Answer Correct ? | 0 Yes | 0 No |