wt is cold junction compensation
Answer / d tilston
Cold junction compensation is required when using a
thermocouple, (TC) to measure temperature.
A TC uses two different types of metal to produce a very
small voltage. This voltage varies as the temperature
changes. The wire used on TC must be the same material as
the TC itself, otherwise you have just created another TC.
The voltage from the second TC will cause errors in the
reading from the first TC. When you get back to the device
that is interpreting this small voltage, you will be
connecting it to the copper on the boards of that device.
As stated earlier, this will create another two TCs, one for
each wire, but if your know the temperature at the device,
you can compensate for these additional voltages. That is
where the cold, (not in the process) junction compensation
is required.
| Is This Answer Correct ? | 0 Yes | 2 No |
Need Intergraph softwares like SPI(INTOOLS),sp3d,PV ELITE, SP P&ID. CONTACT : logu.2211@gmail.com (8867825756)
Dear Friends, we are planning to design Power distribution and Fiber optic in the same cabinet.Like Front side Fiber optic and Rear side Power distribution.Is it any possibility of problem occurs like interference etc? Your answer is highly appreciate.
can we create an interrupt in plc through scada?
The process variables that need to monitored and controlled are ________, ________, _________ and
Dear all... I have 1 0-400 duplex type RTD, I connected the A side to the temperature indicator and B side to the PLC panel, but when I have observed then found that The PLC side temp has the variation. and it was distub to other RTD temp also. so what can I do.pls help me
how to do dynolab wind speed sensor loop test, how to simulate value,i have simulate mA 4-20mA but not responding in DCS faceplate, please kindly advice me any one.
Functions of electropneumatic valve positioner:
I am a electronics and instrumentation fresher trying for a job in IT sector. what do need to prepare for the interview?
I have installed a RTD whose length is 2250mm(RTD stem length), but it's upper 200 -250mm is out of the reactor, and this upper 200mm stem is surrounded by atmospheric temp. And the lower portion i.e. 2000mm is in contact with the measuring fluid, then does the final measuring temp. Gonna change as the upper 200mm RTD stem is out of reactor?
1 Answers Process Control Technologies,
What is difference between reset and initialization in industrial automation?
How to calibrate radar type level transmitter for interface level? Total liquid(liq.1 and liq.2), level both the liq individually? For. Both the liquid levels how the signal will go from transmitter to dcs? How to calibrate. Single radar 9:26:55 AM for 2 different liquids in a tank?
0 Answers Almeer Technical Services,
what is actual difference between pressure Transducer & Pressure Transmitter.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)