hello every one,
what is the difference between the Kvar and farads, Rating
on Power capacitor is for eg: x kvar, and normal capacitor
is eg: x farads.
what is the relation between these two?
Answers were Sorted based on User's Feedback
KVAR : stands for Kilo Volt Ampere Reactance , used to
measure maximum reactive power (imaginary) that can the
capacitor stands
Farad : unit of measuring the capacitance of the capacitor
Depends on your source voltage and frequency.
VAR = reactive power = V*I (for a capacitor)
For a capacitor in a steady state AC circuit, V = I/(jwC) =
I/(2*pi*f*C) or I = 2*pi*f*C*V
Substituting, then
VAR = C*(2*pi*f*V^2)
kVAR = VAR / 1000
| Is This Answer Correct ? | 4 Yes | 1 No |
kvar-kilo volt ampere with reactive component
farads-unit for capacitor
a set of x farad capacitor can develop y kvar capacitor bank
for power factor correction.
kvar-unit of reactive power developed by capacitor bank for
power factor correction
kva2=kw2+kvar2
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / vanika jain
KVAR is the unit of reactive power which is generally used to magnetise the circuit and power capacitor is one of those equipment which provides reactive power and therefore its mentioned in kvar,i.e. its rating. farads is the unit of capacitor and is used normally to denote the rating of normal capacitor.
| Is This Answer Correct ? | 0 Yes | 1 No |
what is the formula for transformer oil?
Which test will be more severe for VCB?
what is diff b/w electrical & electronics ?
my name is venkat .i have good percentage in my academics(ssc 86, intermediate 83 b.tech 73) my question 1..after completion of my ssc i joined in bpc but i didnt got rank in emcet so i completed MPC in one year compartmentally ..so here what am expect question from this background?
Q.1:What protection will be used on HT and LT side of 33/0.4 KV, MVA transformer. Indicate capacities of protective device to be used. Q.2:Which types of back-up protections are used in the power transformers? What do you understand by the term over travel in the relay? Q.3:How star and delta connected winding transformer are provided from earth fault
What is substation?
WHAT IS THE PARTIAL DISCHARGE TEST?
How much KVAr bank reqired for 630 KVA transformer on full load for maintain power factor upto.99
4 Answers Dhanalakshmi Industries, DLF,
can I connect step down transformer(25KvA,240V Phase to phase)to output of online UPS(15KvA,440V PHASE TO PHASE) Load connect to TRANSFORMER is 13KvA,240V PHASE TO PHASE. please brief if it is wrong
What do you mean by the zone of protection?
what is PI value and its significance for insulation testing?
In a parallel circuit dc circuit with two resistors, if you know the voltage, amperage, and one resistors ohms, what formula is used to find the second resistors ohms?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)