( Re: WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR
CAPACITOR BANK
Answer
# 1 The capacitor current would be kvar x 1000 / (415 x
sqrt3). This would be 70a approx. The MCCB selected should
have *atleast 1.4 times this current i.e. 1.4 x 70= 98. So
you should choose at least 100 A mccb.)
regarding to this answer,i would like to know why the
current have to times 1.4 to get the right amphere for the
mccb.hows the formula to get the 1.4??tq
Answers were Sorted based on User's Feedback
Answer / silu pattanayak
While switching the Capacitor, a charging current of 1.4 times the rated value will be taken by the capacitor due to the "transient" phenomena arising during switching. Therefore, a factor 1.4 is used as safety factor to avoid unnecessary tripping during switching.
Is This Answer Correct ? | 0 Yes | 1 No |
if the capacitor bank is 525v??izzit the calculation same
as 440v??
Is This Answer Correct ? | 0 Yes | 4 No |
motor is 12.5hp after starting few minets motot get hot? why?
I want to replace the 3 KW DC motor with AC motor so what should be the rating of AC motor? Details Of DC motor to be changed with AC are - Kw - 3, Vf - 310, If - 0.15, Va - 400, Ia - 13, RPM - 2400
Two electric lamps 40 W, 220 V each are connected in series across 220 V. What is the power consumed by the connection?
why transformer ratinh is in KVA????/
8 Answers Apollo, Priyadarshini, Reliance,
what is cable meggering formula for low voltage ?
why transformer not used to starter
Dry type transformers
What is the max value of neutral current that can be allowed in system?
what happens if sf6ckt breaker gas pressure is high or low about the actual rating of gas pressure(5kg/cm2)
why we use 3 phase in our country?..why no 4,5 or 2??
What is the difference between AVR and Servo Stabliser
what is working of communitator in a dc generator?