( Re: WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR
CAPACITOR BANK
Answer
# 1 The capacitor current would be kvar x 1000 / (415 x
sqrt3). This would be 70a approx. The MCCB selected should
have *atleast 1.4 times this current i.e. 1.4 x 70= 98. So
you should choose at least 100 A mccb.)
regarding to this answer,i would like to know why the
current have to times 1.4 to get the right amphere for the
mccb.hows the formula to get the 1.4??tq
Answers were Sorted based on User's Feedback
Answer / silu pattanayak
While switching the Capacitor, a charging current of 1.4 times the rated value will be taken by the capacitor due to the "transient" phenomena arising during switching. Therefore, a factor 1.4 is used as safety factor to avoid unnecessary tripping during switching.
| Is This Answer Correct ? | 0 Yes | 1 No |
if the capacitor bank is 525v??izzit the calculation same
as 440v??
| Is This Answer Correct ? | 0 Yes | 4 No |
explain different losses in a transformer.
How to implement 6 output with 3 input NAND gate?
In India the supply voltage is 230 volt A.C. During the negative half cycle phase becomes neutral and neutral become phase? or what will happen during negative half cycle? how the electrons flow during positive and negative half cycle?
If more than rated DC voltage appears across trip coil of the breaker, what will happen? e.g. in 110V DC circuit system, if voltage across battery terminal showing 121 V
what is single turn and multiturn encoder ? Can single turn encoder be used to show rpm of a motor(on shaft) ? Plz explain in brief .abanirout@gmail.com
which network topology offers the greatest level of tolerance?
What will be the current after disconecting the bus bar or cable before discharging ?
what happen ,if generator will generate leading power factor?
electrical engineering giving priority for insulators rather than conductors, why ?
If the line voltage is reduced to 75% of its rated value then by what percentage current will reduce ?? 75% 25% 50% no change and why ?
1.Can we use 6.6/11KV 300sq mm xlpe 3core cable for LT use (415 Volt). 2. If we use it for LT then what is the current rating
How to know vacuum in vacuum cylinder of breaker in working condition
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)