Answer / varun
The main difference between normal motor and flameproof motor is the construction of the frame of the motor. Electrically the 2 motors are identical (depending on the manufacturer and money)
The flameproof motor's frame is more robust with larger spigots and end caps on the bearing housing. This more robust frame is needed if a gas explosion (not electrical explosion) occurs inside the frame of the motor, the explosion needs to be contained inside the frame and the flame need to be cooled down by the time it reaches the outside.The larger spigots on the frame is acting same as a cooler for the flames (this is called the flame path).
The sizes of the spigots are determined by the volumetric capacity of the frame, in other words the larger the frame size the larger the spigots. This effectively is needed because the more gas that will be able to gather in the frame of the motor, the bigger the explosion will be, the bigger the spigots needs to be to create a longer flame-path to cool the flame down.
| Is This Answer Correct ? | 23 Yes | 4 No |
FOR WHICH FAULTS OR CONDITIONS DOES A TRANSFORMER DIFFERENTIAL PROTECTION DOES NOT OPERATE???
what is different between DIGITAL and ANALOG?
when we r using 3.5 cable for a bldg. and put laod on each phase using the neutral and neutral is the return paht for the phase so the current of the neutral must be Ir+Ib+iY (return).But the size of the netural is .5 as comper to the phase.
Is there a chance for a motor speed to become negative..?? What is the reason for such a phenomenon.? In that case does the motor works as a generator..???
how synchronous generator can be used as synchronous condenser?
STATE AND EXPLAIN SUPER POSITION THEOREM.
why neutral busbar size is half of the phase busbar size in control panels
HOW TO WRITE A QUENTION ANSWER? I MEAN SHORT OR LENGHTHY ? OR FROM THE BOOK AS BOOK..... SOME TIME WE GIVE A ANS FROM THE BOOK AS LIKE BOOK ND WE GET MINIMUM 60% MARKS OR MORE THEN....... THEN HOW TO FILL THE Q-PAPER?
How to do maintenance of transformer feeder.
A 200 KVA UPS's load current is 70 A. We want to provide a Generator back up. What capacity of DG required for this ?
Can we use the Poly Phenly Sulphide instead of Poly Phenly Ether? Do clarify your opinion.
Can I use measuring current transformers in protection purposes?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)