Answer / kajanijam
If we use protection CT for metering purpose,its core has high saturation point.if any fault occurs, the core is not saturated.so it will damage the meters connected to CT secondary
and if we use metering CT for protection purpose,its core has low saturation point,so CT core saturated low value of current,so relay will be inoperative
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sujeet pandey
Measuring CT needs to be very precise so its coil are better
quality than the protection CT. In case of wrong
connection,there will wrong reflection of primary current
which is not desirable.
Is This Answer Correct ? | 2 Yes | 3 No |
If an induction motor is restarted before its rotor stop rotating, then what will be the amount of current drawn? Is this current will be the same as motor starting current?
i am working in automation feild my question is that how to find the KVA of transformer.
which circuit breaker enclosure is best for maintenance guy? 16 bolt & 20 bolt squre or 16,20 bolt hinge
at meter room 50 hrc switch installed,but there are not get earthing proper,so what happen?and 11kv transformer out put going in to hrc main 400a three nog each? so earthing is require for all switch? (some customer made earthing at there home.)
0 Answers Ebrahim Textile, Siemens,
would the same effect be achieved by reversing the connection to one winding of the induction motor 3-phase?
what is the use of vcb & isolator in substation?
What are electric motors?
i need list of swg(standard wire guage) or area of conductor v/s current carrying capacity of conductor copper & alluminium...
why 3 phase induction motor only need starter ? why not other motors need starter ?(like synchronous motor,single phase induction motors & their types) ?
why do we prefer -48 volt instead of -24volt or -12 volt etc. ??
why does a dc machine has high efficiency while working as a generator than as a motor ..
A 100 kVA , 400 v/250 kv testing transformer has 8% leakage reactance and resistance on 100 KVA base . A cable has to be tested at 500 kv using the above transformer as a resonant transformer at 50 hz . if the charging current of the cable at 500 kv is 0.4 A find the series inductance required . Assume 2% resistance for the inductor to be used and the connecting leads . Neglect dielectric loss of hte cable . what will be the input voltage to the transformer ?