what happend if the protection ct is by mistake put instead
of measuring ct & vice versa?
Answers were Sorted based on User's Feedback
Answer / kajanijam
If we use protection CT for metering purpose,its core has high saturation point.if any fault occurs, the core is not saturated.so it will damage the meters connected to CT secondary
and if we use metering CT for protection purpose,its core has low saturation point,so CT core saturated low value of current,so relay will be inoperative
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sujeet pandey
Measuring CT needs to be very precise so its coil are better
quality than the protection CT. In case of wrong
connection,there will wrong reflection of primary current
which is not desirable.
Is This Answer Correct ? | 2 Yes | 3 No |
How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be cablesize? What are the points to remember for cable sizing calculations?
We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Make Atlas Copco 5.5 kva) that time we face the lot of fluctuation on Dg output. Can you please suggest me how can prevent this fluctuation?
plz send me the placement interview question and answers of whizchip(technical and apttitude)..i have an interview in next.
What is the criteria in selecting Air circuit breaker(ACB) & Moulded case circuit breaker(MCCB) for a particular range?
What is a LBB protection and why it is used?
Convert a star connected network into a delta connected network.
what is the difference between star and delta connection?
How to differentiate 220 Kv & 132 Kv line transmission tower if there are no specifications given on towers?
What is creepage distance..... what will be the value for different voltage level
what is the difference between ac motor and dc generator
why 15 kw motor winding resistance is low then 5 kw motor winding resistance?
WHEN SINGLE PHASE SUPPLY AS 220V, WHY THE 3 PHASE- 4 WIRE MEASURED AS 440 VOLTS INSTEAD OF 660 VOLTS (220 VOLTS PER PHASE i.e 220x3 = 660 volts ).