I want to know what must the CT ratio be on a load of 300A
is a 3PH nutral to earh installation?
Answers were Sorted based on User's Feedback
Load current is 300A. The equipment shall withstand the
starting current -which is around -5-8xIn.It is preferable
to select 1ooo-1200A/1A OR 5A.
WE ADOPT THIS THUMB RULE for our protection setting& co-
ordination.
| Is This Answer Correct ? | 0 Yes | 0 No |
The neutral is a point in power transformer or in motor
connection where all phases are connected.In this point
voltage is zero. when you connect thisoint to earth, the
fault current or capacitance circulating current flows to
earth.
when a fault occurs , current is high.Therefore,CT ratio
should be 1000-1200/5 or 1A.
It is usually upto designer or protection device supplier.
| Is This Answer Correct ? | 0 Yes | 1 No |
What is meant by positive and negative feedback?
what is meant by tranformer impedance?
What are the different sizes of cables for H.T and L.T side of supply?
7 Answers Bhel, BSES, Karthik Industries, Lanco, Nedco, Shilpa Electrical Engineers, TATA, Torrent Power,
name the famous power plants in ap and vwhere it is located with capacity details
How much KVAr bank reqired for 630 KVA transformer on full load for maintain power factor upto.99
4 Answers Dhanalakshmi Industries, DLF,
Dear Sir / Madam, Actually we requied 64 A MCB, But i have 32 A MCB = 2 No's this two i have to make series connection and we usw any place? isit possible or not......
4 Answers Hindustan Unilever Limited,
what is Over current, earth fault (O/C+E/F) ?
we all know that corona is nothing but ionization of air around the conductor and there by allowing current to pass through ionized air.but we are not getting any short circuit in between the respective phases though the air turned as a conductive media between them??
wht d.c produces corrosion
What, in the construction of a transformer, controls KVA? For example 600/208/120 V transformer can be 10kVA or 45kVA!!! What do we change in the construction of a Transformer in order to change the rating but not the voltage.
how manyunits consumed by 25 kvar capacitor bank
In separately excited m/c,we excite the field by a dc source,what not with ac source?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)