generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?

Answers were Sorted based on User's Feedback



generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same ..

Answer / carl_ellis

Yes, V=IR, but that happens because the transmitter
functions as a transistor, varying its resistance in order
to regulate the loop current.

It is expected that the power supply voltage remains constant.

The transmitter acts as a transistor and regulates the loop
current as long as there is sufficient power supply voltage
to drive the current through the loop resistance (ohms law).
If the power supply voltage is not adequate, the loop
current will be limited to something less than a full 20mA
and in some cases the transmitter power-cycles itself and
starts through repeated initializations, trying to drive
current, but failing to do so.

Changing the power supply voltage will not change the loop
current as long as the power supply voltage change is above
the minimum needed, because that is the design
intent/purpose of 2 wire loop transmitters: to regulate the
loop current to match the process variable the transmitter
is measuring. Any excessive power supply voltage is
'dropped' in the transmitter in order to regulate the loop
current.

Every 2 wire loop powered transmitter has either an equation
for calculating the voltage required for a given loop load
resistance or a graph called a 'load line' that shows
voltage versus loop resistance. The minimum required
voltage to light up the transmitter is called "lift-off"
voltage, which is the minimum required when a power supply
is directly connected to the transmitter, like on the shop
bench, with no load; no analog input, no appreciable wire
resistance.

A typical 24Vdc power supply will drive 500 ohms of loop
resistance with most 2 wire transmitters.

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 0 No

generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same ..

Answer / manohar m chotrani

In an electronic transmitter power supply varies with the
load attached.Normal power supply is 24V DC for a
transmitter. of this 12 volts are required to run the
transmitter without any load.This will give 4-20 mA as
output as we go on increasing the load we have to increase
the supply voltage to get a 4-20 mA current. Every load of
50 ohms require 1 volt increase in the supply voltage but
upto a certain limit like ABB made transmitter can take load
upto 2020 ohms with the 55 volts as supply.Beyond 55 we can
not increase the supply because operating voltage is 12-55
volts. If we increase the load beyond 2020 ohms with 55
volts current output will be affected.There is no voltage
regulator in the transmitter

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

What is difference between differential pressure & delta pressure?

0 Answers  


wt is cold junction compensation

1 Answers  


What for barriers are used in DCS & PLC systems?

2 Answers  


how to calibrate temprature switch and flow switch ?

1 Answers   Adgas,


how to solve temperature error in compressor?

1 Answers  






In oil & gas industries and petrochemical industries, there are classification of zones like zone 0, zone 1, zone 2. Is there any differences in voltages or power supply supplied for the process instruments, control instruments depending on the zones

1 Answers  


Draw a complete P&ID of a flow suction tank indicating all control & protection equipment. Indicate all its inlets and outlets. Explain the controls for this system

0 Answers  


how to overhaul control valves.what are the proper procedures.

1 Answers   Jindal, QAFCO,


Working principle of vibration sensor?, Type of vibration sensor? , Can we use vertical instead of horizental or vice versa?, if not Reasons?

2 Answers  


when the operation engineer told you that he gives the control valve order to open but there is no response ! what will you do ? and if you found that there is astuck , what will you do ? (note : it is apanumatic valve )

5 Answers  


what is the difference between SMART and tipical transmeter ?

3 Answers   Sirte Oil Company,


Why drum level range is given -500 to 0 mmwc pls give me that answer

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)