Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?

Answer Posted / carl_ellis

Yes, V=IR, but that happens because the transmitter
functions as a transistor, varying its resistance in order
to regulate the loop current.

It is expected that the power supply voltage remains constant.

The transmitter acts as a transistor and regulates the loop
current as long as there is sufficient power supply voltage
to drive the current through the loop resistance (ohms law).
If the power supply voltage is not adequate, the loop
current will be limited to something less than a full 20mA
and in some cases the transmitter power-cycles itself and
starts through repeated initializations, trying to drive
current, but failing to do so.

Changing the power supply voltage will not change the loop
current as long as the power supply voltage change is above
the minimum needed, because that is the design
intent/purpose of 2 wire loop transmitters: to regulate the
loop current to match the process variable the transmitter
is measuring. Any excessive power supply voltage is
'dropped' in the transmitter in order to regulate the loop
current.

Every 2 wire loop powered transmitter has either an equation
for calculating the voltage required for a given loop load
resistance or a graph called a 'load line' that shows
voltage versus loop resistance. The minimum required
voltage to light up the transmitter is called "lift-off"
voltage, which is the minimum required when a power supply
is directly connected to the transmitter, like on the shop
bench, with no load; no analog input, no appreciable wire
resistance.

A typical 24Vdc power supply will drive 500 ohms of loop
resistance with most 2 wire transmitters.

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is 3 selection available when configure the burnout protection for controller

2676


why we use 3 wire rtd direct wiring for temperature measurement instead of temperature transmitter like bearing temperature

1802


What is difference between Ionization heat and bimetallic heat

1623


how pressure transmitter work, what is its principal to measure and how its generate signal. for pressure transmitterinstallation which precautions must be taken ??

1730


How hart protocol can be connected with control valves?

1025


what is the procedure of O2 sensor(ABB) calibration?

2173


Which topics are covered in Process Control?

2135


How many interlocks at turbine side?

1910


what does the ratio 800-400-300-200/1-1-1-1-1 in the specification of current transformer indicates?

2505


Capacitance, resistance ( colour coding ), parallel & series circuits.

2202


explain key exchanges in all security modes WPA,WPA2,TLS?

2015


Draw a group of instruments interlocked to a Pump & Motor?

1282


Which tank weighing system is better to install (Accuracy point of view) 1) Tank weighing system with 3 load cell or 2) Tank weighing system with 4 Load cell

1292


What is 1:1 redundancy ?

2366


field bus transmitter calibration procedure tell me

1817