control valve in manual/auto mode huntting checked spring
tention also it is ok.positioner also good condition &
incoming inst air line also constant pr.kindly give us
correct answer?
Answers were Sorted based on User's Feedback
Please check following things:
1. To loose gland packing, due to tight packing, valve may hunt.
2.Check leakage from diaphragm.
3.May be seat or plug loose
4. Check cut marks at feed back linkages.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / gopalakrishnan.p
Kindly check the following thigs for betterment
1.Loop tune ur controller.(gain value,integral
time,derivative time).
2.Check the cable(connector side ..i,e may be loose
connection).
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ashish namdev
Kindly check these following :-
1. first check positioner link spring.
2. adjust link assembly.
3. adjust instrument air at valve specified pressure
through AFR.
4. check all parameters and settings in positioner.
5. give auto calibration command and calibrate it.
6. Tune your controller.(gain, PID controlling)
Is This Answer Correct ? | 2 Yes | 0 No |
please check followings:
1-check gland packing if tight then may be loose.
2-If booster relay installed then check its equlizer valve
some time this valve called by-pass valve.The valve may
adjut to approprite position as hunting stop.
3-Check feed back linkage with touch any part of the body.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / imran
First check its feedback link spring if it is ok then
checked its feedback potentiometer by removing it from
positioner with meter.these r main causes that already i
faced.
Is This Answer Correct ? | 0 Yes | 0 No |
I want to know if flowrate increases in 16' pipe line what will happen to upstream pressure and why?
how commission a transmitter evev plant is already running
in i/o panel for digital ouput(do) how much power(in volts) we must give?
what is instrumentation?
What FLOW METER generally used in Gas plant?
WHY RESISTANCE TEMPERATURE DETECTOR IS AN ACTIVE DEVICE
if my 6 kva UPS gives 20 min. backup at 100 % load, then at 25% load what is the backup time?
in split range control system we are using two control valves,but we have only one positioner and one feed back link.so how we use this one feed back link for two control valves?
We have yokogawa cs3000 one fcs and 4 his. After download to his, showing successfully at es, but not transferred to his.
where we are used split range control
How Honeywell FSC is functioning and what is its purpose? Can we bypasa it and only use DCS instead of that.
Linear amplifier.