control valve in manual/auto mode huntting checked spring
tention also it is ok.positioner also good condition &
incoming inst air line also constant pr.kindly give us
correct answer?
Answers were Sorted based on User's Feedback
Please check following things:
1. To loose gland packing, due to tight packing, valve may hunt.
2.Check leakage from diaphragm.
3.May be seat or plug loose
4. Check cut marks at feed back linkages.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / gopalakrishnan.p
Kindly check the following thigs for betterment
1.Loop tune ur controller.(gain value,integral
time,derivative time).
2.Check the cable(connector side ..i,e may be loose
connection).
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ashish namdev
Kindly check these following :-
1. first check positioner link spring.
2. adjust link assembly.
3. adjust instrument air at valve specified pressure
through AFR.
4. check all parameters and settings in positioner.
5. give auto calibration command and calibrate it.
6. Tune your controller.(gain, PID controlling)
| Is This Answer Correct ? | 2 Yes | 0 No |
please check followings:
1-check gland packing if tight then may be loose.
2-If booster relay installed then check its equlizer valve
some time this valve called by-pass valve.The valve may
adjut to approprite position as hunting stop.
3-Check feed back linkage with touch any part of the body.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / imran
First check its feedback link spring if it is ok then
checked its feedback potentiometer by removing it from
positioner with meter.these r main causes that already i
faced.
| Is This Answer Correct ? | 0 Yes | 0 No |
if we mount flow tube in arrow direction then flow comes in negative & if we mount it another direction then flow comes positive,So what will be the problem
Isometric drawings are generated during _________________ phase of a project
what is the difference betwwen the 2wire level transmitter and 4wire level transmitter??and their applications also??
what is lead lag compensator and for wat v using that???
Hi Frnds , If Suppose 1 Pair cable of 1.5 sq mm is used for Transmitter and instead of 1.5 sq mm if i used 0.5 sq mm cable will the resistance change will occur and does it affect our transmitter reading. plz mail ur answer to ntnkamble@gmail.com plz immediately mail ur reply
If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , then it will reaches again 50%, this type of action occured frequntly.. so what to do for solve this problem. The possible cause is in volume booster or positioner's relay.. positioner is double acting .. and make siemens..sipart.The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?
2 Answers Gujarat Fluorochemicals Limited (GFL), Shell,
Boiler flame scanner working principle?
what difeerent between HART and BRAIN?
what is difference between 3 wire and 4 wire RTD sensor?
12 Answers HTA Instrumentation,
pls suggest suitable MOC of diaphragm for pressure measurement of UREA grade solution service fluid.
can any one tell me when ongc placement test and its forms is available????/ pls tell me if u know
why relays are used with plc?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)