There is 3phase power cable from 1 point to the other point
which is 100m away. Two point equipped with power meter and
recorded 1st point is 205kW while the 2nd is 202kW and each
phase average carry 400amps. To calculate the resistance of
the 3phase power cable, is the formula using will be P=I2R?
Answers were Sorted based on User's Feedback
Answer / pdbhatt69
If total loss in cable is 3 Kw hence it must be devided n
al 3 phases and hence 1 KW loss in one phase, now you can
use frmula P=I*I*R.It comes around 2.083 Milli ohm.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shyamkr
i think the current I will be the r.m.s value of current not
he average value and P will be the power loss in the cable.
so the formula P =I(r.m.s)2 * R.then this formula will give
the resistance in the ac circuit.
Is This Answer Correct ? | 0 Yes | 1 No |
every motors written in name plate IP 55 what is this?
Explain the advantages and disadvantages of thermal power plant?
why surge protectetor work explain with the help of circut diagram?
How can we calculate No load and full load torque of electrical machines, i.e. motor or alternator?
If NO contact of relay gets supply from other sources or other part of circuit and at a time relay coil activates,then current will flow in which direction & will it cause to damage relay??
how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec.
1 Answers Bhel, Indorama, Power Grid,
why synchronous motor is not self starting
what is XLPE cable?
whats is the role of power factor in designing a tariff structure?
what is cogging and crawling
can we run a motor rated 50Hz,415vac,1440RPM At higher speed then rated on name plate with the help of VFD /drive on long term basis.wheater it will effect the motor life
how do you tell if a avalanche button diode is a p or an