There is 3phase power cable from 1 point to the other point
which is 100m away. Two point equipped with power meter and
recorded 1st point is 205kW while the 2nd is 202kW and each
phase average carry 400amps. To calculate the resistance of
the 3phase power cable, is the formula using will be P=I2R?

Answers were Sorted based on User's Feedback



There is 3phase power cable from 1 point to the other point which is 100m away. Two point equipped..

Answer / pdbhatt69

If total loss in cable is 3 Kw hence it must be devided n
al 3 phases and hence 1 KW loss in one phase, now you can
use frmula P=I*I*R.It comes around 2.083 Milli ohm.

Is This Answer Correct ?    1 Yes 0 No

There is 3phase power cable from 1 point to the other point which is 100m away. Two point equipped..

Answer / k.prakashchandra

Yes

Is This Answer Correct ?    0 Yes 0 No

There is 3phase power cable from 1 point to the other point which is 100m away. Two point equipped..

Answer / shyamkr

i think the current I will be the r.m.s value of current not
he average value and P will be the power loss in the cable.
so the formula P =I(r.m.s)2 * R.then this formula will give
the resistance in the ac circuit.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

i need to calculate high voltage line power factor daily basics but there is meter reading kwh and kvah while calculating power factor kwh/kvah formula was right. for examble there is point c=13kwh c=1.8 lag c=1.2 lead and c=14.5kvah like that i know that p.f =kwh/kvah but c=1.8lag kvarh and c=1.2lead kvarh points i dont know if u know please reply

1 Answers  


IT IS DESIRABLE THAT THE INCOMING MACHINE SHOULD BE A LITTLE FAST AT THE TIME OF SYNCHRONIZING.EXPLAIN?

1 Answers  


What is the SCR system in drilling rig.

2 Answers   Weatherford,


How to set the relay,,??

0 Answers   Megatron Solutions, Nestle,


In a generator (Synchronous) does the rotor speed (frequency) corresponds to the speed of the water (in hydro). does the torque on the turbine relate to the flow of water?

2 Answers  


why we use ac system in india why not dc

3 Answers  


how to calculate the current carrying capacity of cable

2 Answers   Bhel,


how to calculate cable bending angle in a trench?

2 Answers   Eastern Cement,


Define steady state error.

0 Answers  


If I have a motor of 1MW with 6.6kv, running at 35% load, how can i save energy without reducing the load ?

2 Answers   Reddy Labs,


how to find out difference between ELCB, MCB and RCB on looking on it

1 Answers  


why would amp draw on neutral wire be as much as amp draw on the hot leg.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16637)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)