What is meant by operating sequence of VCB : 0–0.3sec.–CO–
3min.-CO
Answers were Sorted based on User's Feedback
Answer / srinivasan.
open-300 millisec-Close /open-3min-Closeopen - means the
circuit breaker is capable of performing the above
operations even at full shorcuit currents.
At the same time the circuit breaker should not be allowed
to operate lesser than these timings.For example open-20
millisec-Close open-1 min-close/open.
This type of breakers are called single shot autoreclose
breakers.
Immediately after a fault breaking,we can do close open the
circuit breaker.
This sequence is tested during type testing only.
Is This Answer Correct ? | 16 Yes | 3 No |
in railways why we use the power in 10,20 30kv,why not in the multiple of 11kv
what is importance of ka in mccb
can you any one give exact mathematical relation between AC current and DC current?
please give me all the Alarm .Trip ,Safety Relays & Conditions of Diesel-generators mail me on ashokbabunhce@gmail.com
Are generator action and motor action relates to a particular machine only?
what are the effects when a salient pole alternator is run at high speed like 3000 r.p.m?
Explain the process of commutation in a dc machine.
what is the difference between between open delta and broken delta?
Application Comparison between 22KV (UE)and 33KV (E) system. Are we allowed to use 33KV (E) cable in lieu of 22KV (UE) cable. What are the technical disadvantages.
america 60hz electric supply is used; but india it is 50hz; why? and if we use 60 hz supply what changeg has to be done or all the equipment has to be thrown which has rating of 50hz frequincy
In 11KV Double pole structure for each phase we are using Disc one Insulator. Why we are not using 2 r above insulators instead of one insulator?
What happened when we give 2 phase supply to a 1 phase equimpent. It's effect on equipment's efficiency and life?