we are operationing 3NOs 800 Kva generators by
singronyus.specialey evening time our panel trip. the panel
showing generator earth fault
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Which relay ? SEFR or back -up EFR ? Are the gens connected
to grid ? Whether all the gens trip simultaneously ?
Whenever there is a momentary heavy earth fault in the
outgoing feeder,all the gens trip on back-up EFR with
instantaneous trip indication,though the line does not
trip.So ,it is advised to disable instantaneous fault trip
i.e. high-set of the back-up EFR.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
Another probability. If there is any earth fault before the
GT primary bushings ,the gen may trip on SEFR if voltage
based( open delta) relay is used.Then you have to check
cable,termination glands and the stator winding for earth
fault either by meggering or better by applying rated voltage.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / biplab
check the stator insulation with megger of each gen........
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ronnie
this might be the result accumulation of moisture near the
earthing bit during evening time.which causes the generator
to trip showing earth fault....
| Is This Answer Correct ? | 0 Yes | 0 No |
Where double earthing is required? Is there any power specification to have double earthing?
What is the role of a Production Engg in a Industry?????
For 415v,3phase,22kw rating of motor how to calculate MCCB rating
Supose we have one 220v A.C fan.if we provide 220v D.C what will be happen?
if transmission voltage expressed as the multipple of form factor(1.11)........11,33,66,220 etc......then why madakkathara substation(kerala) voltage is 400kv..not 440.....?
why ct ratio always rated 5.
FRIENDS, I am doing DEEE (part time)final year. Give me some ideas for project
What do you mean by distributed winding in alternators? how exactly is 3 phase power generated?
Can a 50-Hz designed transformer be used at 60-Hz system? Is the same remains true, when a 60-Hz designed transformer be used at 50-Hz system? Consider only frequency variation. The voltage remains as rated value in all cases. Justify the answer.
what is the meaning of TPN
What is motor type DG starter
can we use 7volt DC BATTERY to run a 60watt motor by stepup? Give reason for your answer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)