why the autotransformer burnt while stating the pumpmotor?,
In starter and motor there was no abnormality.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Autotransformer is for starting of large motor.If you use a
starter additionally ,it requires a certain minimum voltage
for the hold coil.As this voltage was high enough for heavy
starting current which burnt the autotransformer.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / amit kumar singh
The one reason may be that at the time of starting,
induction motor sucts very high inrush current for the
establishment of magnetic field. Thus the total MVA
requirement at the time of motor starting is about 6 to 7
times the rated MVA of motor (if voltage is considered to
remain constant at the time of starting).
As, a transformer can only withstand 1.5 times its rated
MVA (i.e. also only for short duration), the heavy
requirement of MVA by motor could have damaged the
transformer (in case of failure of tap changer operation to
reduce voltage applied before starting of motor).
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / d.lakshmi narayana
To check the transformer tap voltage
persantage.(or)Unbalance the tap voltage (or)To take proper
tap voltage for motor starting load
| Is This Answer Correct ? | 1 Yes | 1 No |
what is meant by CT`s saturation ? Can we use Metering CT`s with Protetection CT`s ?
sir i applied for hpcl(electrical).i want to know from which subjects most of the technical que will b asked.and pattern of the written test.pls help me
What must be the minimum distance maintained between 2 Generators as per International standards?
hou we find and calculate the maximum lode capesity of transforer?
One VFD is possible to connect two motors at the same time?
what is the mazor difference between the induction transformer and synchonous motor?what is the similarity between them?
why neutral should connect to earth in delta-star type transformer
why generator is star connected ?
What will happened. if we feed 3phase supplay to the stater with out insert the rotor. How much current will flow through the stater winnding?
For household Load of 11Kw supplying 5Nos. 1.5 ton Air conditioners + usual other load what shall be rating of Either ELCB Or ELMCB? Which of the circuit breaker will be a better choice?
when we connect the capacitor banks in series with the circuit?
What is mean by % impedance of transformer? detail explanations expected.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)