Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why the autotransformer burnt while stating the pumpmotor?,
In starter and motor there was no abnormality.

Answers were Sorted based on User's Feedback



why the autotransformer burnt while stating the pumpmotor?, In starter and motor there was no abno..

Answer / pillay

a)Loose terminations at the auto transformer itself .
b)intermittent failure of the change over timer or starter.
c)excessive load at time of starting .
d)insulation failure of the auto transformer.

Is This Answer Correct ?    9 Yes 1 No

why the autotransformer burnt while stating the pumpmotor?, In starter and motor there was no abno..

Answer / k.prakashchandra

Autotransformer is for starting of large motor.If you use a
starter additionally ,it requires a certain minimum voltage
for the hold coil.As this voltage was high enough for heavy
starting current which burnt the autotransformer.

Is This Answer Correct ?    5 Yes 2 No

why the autotransformer burnt while stating the pumpmotor?, In starter and motor there was no abno..

Answer / amit kumar singh

The one reason may be that at the time of starting,
induction motor sucts very high inrush current for the
establishment of magnetic field. Thus the total MVA
requirement at the time of motor starting is about 6 to 7
times the rated MVA of motor (if voltage is considered to
remain constant at the time of starting).

As, a transformer can only withstand 1.5 times its rated
MVA (i.e. also only for short duration), the heavy
requirement of MVA by motor could have damaged the
transformer (in case of failure of tap changer operation to
reduce voltage applied before starting of motor).

Is This Answer Correct ?    3 Yes 1 No

why the autotransformer burnt while stating the pumpmotor?, In starter and motor there was no abno..

Answer / d.lakshmi narayana

To check the transformer tap voltage
persantage.(or)Unbalance the tap voltage (or)To take proper
tap voltage for motor starting load

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what is bushing in transfermor

7 Answers   Bokaro Steel, Visa Steel,


1.what is meaning of curve into a mcb. 2.what is basic reason changing of curve

0 Answers  


please tell me the all the spcications of the 100MW 11KV HYDEL POWER PLANT SPECICATIONS

2 Answers   Bhel,


we change the speed of the synchronous motor by incresing or decreasing a rotor resistance

1 Answers  


stand by earth fault protection (51G) for transformer rating 2000 kVA,Dyn11,33/0.400 V. LV NCT ratio and necessary resistor and metrosil values how to calculate

0 Answers  


what is the difference between MCB & MCCB

3 Answers  


rrb question

0 Answers  


ROC converges if pole and zero lies inside a) origin b) z=1 c) pole d) zero ? Explanation please? if ROC does not converges then?

0 Answers   CCP,


what is the reasons for blowing fuse

1 Answers  


A 6.6 KV motor breaker is try to Drack OUT by me while the motor running. What will Happened? a, will Trip. b,Drack Out lever will not access c, will get shock d, noting will happened

4 Answers  


why the earth conductor in top of the tranmission line ?

2 Answers  


what is the different between DC & AC load Line.

1 Answers   Emarat,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)