why the autotransformer burnt while stating the pumpmotor?,
In starter and motor there was no abnormality.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Autotransformer is for starting of large motor.If you use a
starter additionally ,it requires a certain minimum voltage
for the hold coil.As this voltage was high enough for heavy
starting current which burnt the autotransformer.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / amit kumar singh
The one reason may be that at the time of starting,
induction motor sucts very high inrush current for the
establishment of magnetic field. Thus the total MVA
requirement at the time of motor starting is about 6 to 7
times the rated MVA of motor (if voltage is considered to
remain constant at the time of starting).
As, a transformer can only withstand 1.5 times its rated
MVA (i.e. also only for short duration), the heavy
requirement of MVA by motor could have damaged the
transformer (in case of failure of tap changer operation to
reduce voltage applied before starting of motor).
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / d.lakshmi narayana
To check the transformer tap voltage
persantage.(or)Unbalance the tap voltage (or)To take proper
tap voltage for motor starting load
| Is This Answer Correct ? | 1 Yes | 1 No |
Why is the diffrential protection in DG. What if the CT polarity is reversed while connecting for the same type of protection? How polarity can be made ok?
Why the power generated in dams is complex power? Why the generators in dams cannot produce Real power directly (i.e power which has zero reactive part)?
what are the protection for DG set and why?
1. what is difference between VCB and ACB.how its works please explian.
6 Answers ABB, Accenture, HP, Minda, Mother Dairy, Satyam Pharma,
What are formula we can apply to determine the HT/LT current of 11KV/433V transformer except KVA/LV×√3. ?
What is meant by inverse definite mean time (IDMT)& definitemean time (DMT)?
How are calculated the aluminium busbar cross section area?
We have three phase dg of 12kva rating.If the load of each phase is not constant.That means one phase drowning more load than remaining two phase..Then what will happen to dg?
Buchholz relay is used ………. a) protection T/F b) oil T/F c) Air core T/F
8 Answers Engineers India Limited,
what is an rmu?its circuit diagram.functions
14 Answers CP Bangladesh, Emrill, NDPL,
Why 50hz and 60hz frequencies are used by the world, why they are not taking 55hz?
What Is Connection APFC Panel In Compony.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)