how to claculate earth strip size for 1500kVA transformer
for neutral and body
Answers were Sorted based on User's Feedback
Answer / chandan tripathy
As per IS 3043, Cross Section Area of Earthing Conductor
(A) =(If x√t) / K
Where:
t = Fault current Time (Second).
K = Material Constant.
Example: Calculate Cross Section Area of GI Earthing Conductor for System has 50KA Fault Current for 1 second. Corrosion will be 1.0 % Per Year and No of Year for Replacement is 20 Years.
Cross Section Area of Earthing Conductor (A) =(If x√t) / K
Here:
If = 50000 Amp
T = 1 Second
K = 80 (Material Constant, For GI=80, copper K=205, Aluminium K=126).
• Cross Section Area of Earthing Conductor (A) = (50000×1)/80
• Cross Section Area of GI Earthing Conductor (A) = 625 Sq.mm
• Allowance for Corrosion = 1.0 % Per Year & Number of Year before replacement say = 20 Years
• Total allowance = 20 x 1.0% = 20%
• Safety factor = 1.5
• Required Earthing Conductor size = Cross sectional area x Total allowance x Safety factor
• Required Earthing Conductor size = 1125 Sq.mm say 1200 Sq.mm
• Hence, Considered 1Nox12x100 mm GI Strip or 2Nox6 x 100 mm GI Strips
| Is This Answer Correct ? | 25 Yes | 6 No |
you will follow as per State electricity board norms - 50
x 6 mm Cu for Nu and 50 x 6 mm GI FOR body 0r
you will calculate as per short circuit calculation
Formula 0.0054 x root t x I
Where
t =1 second
I = SHORT CIRCUIT CURRENT
example
Fault current- 33kA( assumed )
0.0054 x root 1 x 33000= 178.2 mm
so you will recommended 50 x 4 mm Cu
| Is This Answer Correct ? | 14 Yes | 9 No |
Answer / k.prakashchandra
For above 750 KVA ,earth lead is determined as per I.S.1886
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / nitin
Mr. Bala,
what is 0.0054factor? Is it root3 divided by current rating
in A/sq.mm? Then for Cu it is 205 A/sq.mm and so root 3
divided by 205 comes to 0.0084. OK?
| Is This Answer Correct ? | 0 Yes | 5 No |
How can we measure MVAR of a 3 phase transformer.....???
What is the basic difference among IPS,UPS,EPS?
fog produced due to?
what is the chemical name and formula of refrigarent R-134a.
Write down the name of 2 lady Bir Pratin of Bangladesh
WHAT IS START TO INDUCTION MOTER IN STAR TO DELTA OF >5HP ?
why the weight of oil in transformer is specified (on the nameplate) in litres as well as kilo grams?
A 12.5 hp slip ring motor taking high initial current and its MPCB is getting open.what may be the reason?
how to calculate the torque of a motor?
Testing report of Earthing of 3.15 MVa PTR.
Define demand factor?
in a induction motor if we put capacitor across it will the power factor of the motor will improve? if yes how
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)