I have observed in field instrumentation work... I remove
the fuse of an analog transmitter then it shows 7.75 kg/sq
cm (which is practically wrong value)in DCS and when put
the fuse it shows 0 in dcs. Then cheach the field
transmitter termination and found moister. clean that and
then it shows 1.1 kg/ sq cm which is right value. Please
describe the above phenomenon.
Answer / carl_ellis
Reason: ground current added to loop current through a
ground created by moisture.
The analog input on the DCS references ground at some point.
The moisture in the junction box or remote terminal panel
makes a connection to a local ground at that point. The
difference in potentials between the grounds causes a ground
loop - current added to the modulated loop current. The
DCS's analog input 'sees' this current, even though the
transmitter is turned off, because the current is driven by
the potential of the ground loop, not the potential from the
power supply.
When the moisture (and hopefully, the dirt) is removed, the
local ground connection is broken and the loop is isolated,
except for the DCS's AI reference to ground. So the DCS AI
'sees' only the loop current modulated by the pressure
transmitter and reports the correct loop pressure.
Some handheld calibration instruments can detect current
leakage in loop powered loops. An example is the Practical
Instrument Electronics (PIE) 334 Plus calibrator.
http://www.piecal.com/products/evolution/334Plus_mA.php
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
Why are the uses 24vdc in industries
What is a snubber circuit?
What is electronics?
What are primary elements of measuring pressure?
what is Least Value of MICROMETER?
Instrument QA/Qc what is the project quality plan?conduit inspection RFI. which documents attache with package?
i am having information technology branh ....... can i prepare for psu exam
How do you identify between actual alarm and false alarm in a Temperature Transmitter in SCADA based Control System
When doing a liquid seal on a differential flow transmitter , most of the time the sealing liquid will be heavier then the process fluid. For wich application will the sealing liquid be lighter than the process fluid if transmitter is mounted below the process line.
What is Predictive Maintenance
1)unmovable objects have frequency or not?if that object have frequency,how do we measure and transmit? 2)how do u measure the continuity without multimeter? 3)we put 24volt dc supply in railway track how many distance it is traveled without voltage drop?
what is the criteria to decide conductor size of a cable ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)