I have observed in field instrumentation work... I remove
the fuse of an analog transmitter then it shows 7.75 kg/sq
cm (which is practically wrong value)in DCS and when put
the fuse it shows 0 in dcs. Then cheach the field
transmitter termination and found moister. clean that and
then it shows 1.1 kg/ sq cm which is right value. Please
describe the above phenomenon.
Answer / carl_ellis
Reason: ground current added to loop current through a
ground created by moisture.
The analog input on the DCS references ground at some point.
The moisture in the junction box or remote terminal panel
makes a connection to a local ground at that point. The
difference in potentials between the grounds causes a ground
loop - current added to the modulated loop current. The
DCS's analog input 'sees' this current, even though the
transmitter is turned off, because the current is driven by
the potential of the ground loop, not the potential from the
power supply.
When the moisture (and hopefully, the dirt) is removed, the
local ground connection is broken and the loop is isolated,
except for the DCS's AI reference to ground. So the DCS AI
'sees' only the loop current modulated by the pressure
transmitter and reports the correct loop pressure.
Some handheld calibration instruments can detect current
leakage in loop powered loops. An example is the Practical
Instrument Electronics (PIE) 334 Plus calibrator.
http://www.piecal.com/products/evolution/334Plus_mA.php
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
What does threshold mean? what does tolerance mean?
Whatis the reset ofset and control system in instrumentation
0 Answers Asyad International Company, CAE, Sugar Factory,
what are the steps I have to deal with?
How r the calculation of process line mpm.
0 Answers Bhushan Power Steel,
can anybody tel me how a vfd or any field instrument communicates/interface with plc/scada/cs.
what is interlock ckt? why it is necessary in industrial machines ?
What is scan time of PLC?
Vibration probe working principle?
An electronic p controller has an input range of 1-5v, and output range of 4-20mA, while testing a step change of 0.4 was applied at the input , the PB setting was 50% ,what should be the change in the output ?
what is meant by Valve reversibility?
what happen if i install my pressure transmitter below the elevation of pipe in natural gas service. Also support your answer
DCS marshilling Cabinet Power supply can be replace during plant running time?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)