I have observed in field instrumentation work... I remove
the fuse of an analog transmitter then it shows 7.75 kg/sq
cm (which is practically wrong value)in DCS and when put
the fuse it shows 0 in dcs. Then cheach the field
transmitter termination and found moister. clean that and
then it shows 1.1 kg/ sq cm which is right value. Please
describe the above phenomenon.
Answer / carl_ellis
Reason: ground current added to loop current through a
ground created by moisture.
The analog input on the DCS references ground at some point.
The moisture in the junction box or remote terminal panel
makes a connection to a local ground at that point. The
difference in potentials between the grounds causes a ground
loop - current added to the modulated loop current. The
DCS's analog input 'sees' this current, even though the
transmitter is turned off, because the current is driven by
the potential of the ground loop, not the potential from the
power supply.
When the moisture (and hopefully, the dirt) is removed, the
local ground connection is broken and the loop is isolated,
except for the DCS's AI reference to ground. So the DCS AI
'sees' only the loop current modulated by the pressure
transmitter and reports the correct loop pressure.
Some handheld calibration instruments can detect current
leakage in loop powered loops. An example is the Practical
Instrument Electronics (PIE) 334 Plus calibrator.
http://www.piecal.com/products/evolution/334Plus_mA.php
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
THE OUTPUT OF A CURRRENT TRANSMITTER OR A PNEUMATIC TRANSMITTER HAS A LIVE ZERO?EXPLAIN
can i get any detail of interview question asked for instrumentation,plc,scada ,dcs..............
How can one improve linearity of an RTD based temperature measurement system?
what is cascade loop and how it work and why it used instead of PID single loop? In cascade, Which loop is faster and slower? Please explain with loop drawing and example...
what is the reset offset and control system in instrumentation
what is modbus,profibus,fieldbus
How to calibrate Magnetic flow Transmitter in Field
How do you troubleshoot accelerometers used in Vibration monitoring/tripping
How does milli volt is created in themocouple?
WHAT PRINCIPLE OF GAS ANALYSER( CO,CO2,N2)
what is instrument philosophy
What is derating factor in Motor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)