in the measurement of voltage in any circuit we measure the
voltage of one conductor with respect to another.
In DC supply we have two conductors namely Positive(+) and
negative(-). if we consider 48V DC across the two
conductors, then if we measure the value on the positive
conductor with respect teo the negative conductor the value
is +48V. if we measure the same value on the negative
conductor with respect to the positive conductor then the
value will be -48V. this 48V is the instantaneous value of
the DC supply.
Where as in AC we have two conductors namely Phase and the
Neutral. always the Phase constitute the current path and
the neutral forms the return path. we say that the AC
voltage is sinusoidal. that is it varies from positive to
negative when seen with respect to the neutral.
its impossible to measure the instantaneous value of the AC
supply bcoz it keeps on continuosly varying. so for the AC
supply we consider the RMS value (Root Mean Square Value)
as the voltage of the supply. so in this case there is
always the same value when measured with respect to any
conductor. so the AC voltage does not have polarity.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / naren
when we are measureing dc voltage in negative circuit we
have -48V DC , but in AC there is no negative supplay and
hance we get 48V AC from Phase to Nutral as well as Nutral
to Phase.
| Is This Answer Correct ? | 2 Yes | 4 No |
what is an invertor A.C.?
HAI,I HAVE 6,60KW MOTOR FEEDERS IN MY MCC PANEL.HOW CAN I DO MY SETTINGS FOR OVERLOAD,SHORTCIRCUIT,GROUNGFAULT,INSTANTANEOUS TRIP FUNCTION IN MY 4000A CIRCUIT BREAKER?
We have 2 no. 4MW DG set. and GEB supply. But, we running, only 1 DG set. when we done APFC/Power factor setting : 0.90, then winding temp. Low. but when setting done : 0.83, then Winding temp. increase. WHY Why ? ? ?, plz give me answer.
How to select cable rating for HT/LT Panels
Why reverse power relay is used?
why we did not get shock by touching +ve OR -ve busbar (Which are going to supply cell voltage) of Rectifier- Tranformer in electrolysis plant?
What are the operation carried out in thermal power station?
WHAT IS THE COMPLETE DEFINATION OF POWER FACTOR?HOW IT CAN BE IMPROVED?AND WHAT IS CAPACITIVE LOD AND INDUCTIVE LOADS
What is current & voltage ? Voltage perform at any load without current or not?
Electrical Diagram of Electric Arc Furance from transformer to Furances
Why in earthing, the earthing plate is put in vertical position? and further what is soft coke that is used in earthing?
how can we save enegry by using VFD for Resiprocating Air compressor which is having more unloading running hours
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)