How many 2 ton window A/c can runs on a 125 KVA generator?
Answers were Sorted based on User's Feedback
Answer / hareesh k.s.
1 ton=1500W(App.)
2ton=3000W=3.75KVA
utility power of generator is 90%=125x90/100=112.5KVA
Therefore,no.of a/c's=112.5/3.75=33
| Is This Answer Correct ? | 39 Yes | 20 No |
Answer / sushovan das
1 Ton = 12000 Btu/hr.
also one Btu/h is equal to 0.293 watts so...One ton = 3.516
Kilowatts
Hence, 2 Ton = 2*3.516 KW = 7.032 KW
Let we take efficiency of Power Generator = 98%.
Hence, 125 KVA = 125*98% = 122.5 KW.
so no of AC can run on a 125 KVA Generator = 122.5/7.032 =
17 (nearest no) (Ans)
| Is This Answer Correct ? | 12 Yes | 12 No |
Answer / engr stev
Here is the answer with Simple Explanation...
Visit the link
http://www.electricaltechnology.org/2014/02/why-AC-rated-in-Tons-Not-in-kW-or-kVA.html
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / alex
You guys are close.
1ton does indeed = 1400 watts (starting power is higher than the continuous 1150 watts). But the power factor won't be 98%, it'll be more like 80%. So the 120kva = 100,000 watts.
2800 watts each works out to 35 or so 2ton window ACs.
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / abhishek
1ton = 1400watts
so, approximately 38A/c can run on 125KVA generator.
| Is This Answer Correct ? | 3 Yes | 8 No |
Answer / girish
50 A/cs of 2 Ton can run smoothly on a 125 KVA generator
| Is This Answer Correct ? | 9 Yes | 22 No |
Can I use less voltage cable for neutral, since the voltage of return path is zero ideally?
Can anybody just suggest about the scope of Electrical design with ETAP software?Just guide me?
Name the test signals used in control system
11kv alternator commissioning test?
Basic laws governing motor and generator
I WANT YHE TECHNICAL AND ELECTRICAL SPECIFICATIONS OF 2x4MW 11KV 2x10MW 11KV 2x25MW 11KV 2x100MW 11KV HYDEL POWER PLANT i.e PROTECTION SYSTEM,MONITORING,CONTROL SYSTEM,GENERATION,SYNCHRONISATION,METERING PLEASE SEND THE DETAILS TO MY MAIL ID SPRAVEEN_222@YAHOO.CO.IN
wht is the purpose of the earth electrode other then earthing
how to calculate the cable size in sqmm if load (kw) is given?
What is the effect on in Zone and out zone fault if Phase side CT is Vk/2<30 mA and Neutral side is CT is Vk/4<30 mA for Transformer REF protection
How to design the earth grid for lightning protection in an industry
what happen if the secondry winding of the transformer is having less no of turns compare to the primery winding.
In an electrical power supply,why if neutral phase of a 3phase supply fail over current occur but if it's single phase supply neutral phase fail low current occur?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)