How many 2 ton window A/c can runs on a 125 KVA generator?
Answers were Sorted based on User's Feedback
Answer / hareesh k.s.
1 ton=1500W(App.)
2ton=3000W=3.75KVA
utility power of generator is 90%=125x90/100=112.5KVA
Therefore,no.of a/c's=112.5/3.75=33
| Is This Answer Correct ? | 39 Yes | 20 No |
Answer / sushovan das
1 Ton = 12000 Btu/hr.
also one Btu/h is equal to 0.293 watts so...One ton = 3.516
Kilowatts
Hence, 2 Ton = 2*3.516 KW = 7.032 KW
Let we take efficiency of Power Generator = 98%.
Hence, 125 KVA = 125*98% = 122.5 KW.
so no of AC can run on a 125 KVA Generator = 122.5/7.032 =
17 (nearest no) (Ans)
| Is This Answer Correct ? | 12 Yes | 12 No |
Answer / engr stev
Here is the answer with Simple Explanation...
Visit the link
http://www.electricaltechnology.org/2014/02/why-AC-rated-in-Tons-Not-in-kW-or-kVA.html
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / alex
You guys are close.
1ton does indeed = 1400 watts (starting power is higher than the continuous 1150 watts). But the power factor won't be 98%, it'll be more like 80%. So the 120kva = 100,000 watts.
2800 watts each works out to 35 or so 2ton window ACs.
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / abhishek
1ton = 1400watts
so, approximately 38A/c can run on 125KVA generator.
| Is This Answer Correct ? | 3 Yes | 8 No |
Answer / girish
50 A/cs of 2 Ton can run smoothly on a 125 KVA generator
| Is This Answer Correct ? | 9 Yes | 22 No |
please send the last 5 years {{{JUNIOR ENGINEER - ELECTICAL, ELECTRONICS RRB CHENNAI and secundrabad}}} TECHNICAL question papers TO MY EMAIL ID dinesh100701@gmail.com
dielectric strength of vacuum is greater than SF6 but for 132Kv uses sf6 breaker & for 33kV uses vaccum breaker why such a contradiction?
2 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
How is earthing done in Aerospace applications such as Flights and spaceships..?
why crgo core is used in transformers?
what the purpose of data retrivala panel in substation
What do you meant by soft start?
difference between temperature sensor and temperature switch
what is the difference between earth and neutral?
Clearly Define Active,Reactive,Apparant power.Which applications used which power above metioned power?
hi frds, i m electrical engineer.can i get cdr for electrical engineer if u have then send me on my mail id its jayesh_ee88@yahoo.com.please help me frds
What are the Formula of computing Back up Time of 500kVA UPS with 4 Battery Banks, each bank composed of 43 pcs of Batteries 12V150Ah. How to compute the Back up Time of UPS? We have also 3X500kVA UPS running in Parallel same composition as I write above.
What is C-factor?why it is required to consider in fault short circuit calculations?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)