Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How many 2 ton window A/c can runs on a 125 KVA generator?

Answers were Sorted based on User's Feedback



How many 2 ton window A/c can runs on a 125 KVA generator?..

Answer / hareesh k.s.

1 ton=1500W(App.)

2ton=3000W=3.75KVA

utility power of generator is 90%=125x90/100=112.5KVA

Therefore,no.of a/c's=112.5/3.75=33

Is This Answer Correct ?    39 Yes 20 No

How many 2 ton window A/c can runs on a 125 KVA generator?..

Answer / bala.a

Mr.das
yourmconversion is wrong bec 1 ton = 3.51 KW is too high ,
generally all the people recommended 1 ton A/C = 1 TO 1.5
kw so please take this type of conversion .

Is This Answer Correct ?    7 Yes 5 No

How many 2 ton window A/c can runs on a 125 KVA generator?..

Answer / sushovan das

1 Ton = 12000 Btu/hr.
also one Btu/h is equal to 0.293 watts so...One ton = 3.516
Kilowatts
Hence, 2 Ton = 2*3.516 KW = 7.032 KW

Let we take efficiency of Power Generator = 98%.
Hence, 125 KVA = 125*98% = 122.5 KW.
so no of AC can run on a 125 KVA Generator = 122.5/7.032 =
17 (nearest no) (Ans)

Is This Answer Correct ?    12 Yes 12 No

How many 2 ton window A/c can runs on a 125 KVA generator?..

Answer / engr stev

Here is the answer with Simple Explanation...
Visit the link
http://www.electricaltechnology.org/2014/02/why-AC-rated-in-Tons-Not-in-kW-or-kVA.html

Is This Answer Correct ?    1 Yes 2 No

How many 2 ton window A/c can runs on a 125 KVA generator?..

Answer / alex

You guys are close.

1ton does indeed = 1400 watts (starting power is higher than the continuous 1150 watts). But the power factor won't be 98%, it'll be more like 80%. So the 120kva = 100,000 watts.

2800 watts each works out to 35 or so 2ton window ACs.

Is This Answer Correct ?    4 Yes 8 No

How many 2 ton window A/c can runs on a 125 KVA generator?..

Answer / abhishek

1ton = 1400watts
so, approximately 38A/c can run on 125KVA generator.

Is This Answer Correct ?    3 Yes 8 No

How many 2 ton window A/c can runs on a 125 KVA generator?..

Answer / girish

50 A/cs of 2 Ton can run smoothly on a 125 KVA generator

Is This Answer Correct ?    9 Yes 22 No

Post New Answer

More Electrical Engineering Interview Questions

Inductor and capacitor ........ power in one phase and ...... it in another phase. if any body found this gaps answer.please sent me to habib_eu2008@yahoo.com

2 Answers  


Why we are getting low voltage in star connection?

2 Answers  


According to conduit size which size wiring & how many wires can we provide wires in conduit & how can we select conduit size accordingly?

0 Answers  


what is the difference between neutral and earth????

4 Answers  


If the rotor pf of a 3 phase induction motor is .866, then what is the phase displacement between stator and rotor magnetic field 1)30,2)120,3)150,4)90 please justify....

2 Answers   GATE,


Why in power plant projects we see DOL starting method used for motors upto 160 kW instead of star delta method

0 Answers   UCC,


what is the AC Plant and how can do the work with parts and picture tell us 150 Tr

0 Answers   Wipro,


what are the reasons of CT circuit faulty in busbar protection scheme?

0 Answers   Getco,


america 60hz electric supply is used; but india it is 50hz; why? and if we use 60 hz supply what changeg has to be done or all the equipment has to be thrown which has rating of 50hz frequincy

1 Answers  


the circuit having same properties in either direction is known as.......

2 Answers  


HOW TO CALCULATE THE VT SIZING?

0 Answers   L&T,


why we use sinosidal voltage / current instead of others in system?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)