Answer / hareesh k.s.
1 ton=1500W(App.)
2ton=3000W=3.75KVA
utility power of generator is 90%=125x90/100=112.5KVA
Therefore,no.of a/c's=112.5/3.75=33
| Is This Answer Correct ? | 39 Yes | 20 No |
Answer / sushovan das
1 Ton = 12000 Btu/hr.
also one Btu/h is equal to 0.293 watts so...One ton = 3.516
Kilowatts
Hence, 2 Ton = 2*3.516 KW = 7.032 KW
Let we take efficiency of Power Generator = 98%.
Hence, 125 KVA = 125*98% = 122.5 KW.
so no of AC can run on a 125 KVA Generator = 122.5/7.032 =
17 (nearest no) (Ans)
| Is This Answer Correct ? | 12 Yes | 12 No |
Answer / engr stev
Here is the answer with Simple Explanation...
Visit the link
http://www.electricaltechnology.org/2014/02/why-AC-rated-in-Tons-Not-in-kW-or-kVA.html
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / alex
You guys are close.
1ton does indeed = 1400 watts (starting power is higher than the continuous 1150 watts). But the power factor won't be 98%, it'll be more like 80%. So the 120kva = 100,000 watts.
2800 watts each works out to 35 or so 2ton window ACs.
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / abhishek
1ton = 1400watts
so, approximately 38A/c can run on 125KVA generator.
| Is This Answer Correct ? | 3 Yes | 8 No |
Answer / girish
50 A/cs of 2 Ton can run smoothly on a 125 KVA generator
| Is This Answer Correct ? | 9 Yes | 22 No |
What is meant by full pitched winding?
what is meant by switch fuse unit ?
3 Answers Thermal Powertech Corporation India Ltd TPCIL,
how many current required for hypo test
How to solve the problem of low voltage at consumer end in distribution system if one phase come low voltage of transformer
before transformer oil dielectric strenght tests are taken the oil should be allowed to settle to remove option 1 air bubbles 2 gasses 3 contamination 4 water
what is the difference between MCCB and SFU in terms of their application?
2 Answers Secure Meters, Tata Teleservices,
why in generating station generation voltage is 11 kv
can anyone explain 11kV 3core cable megger,hi pot test procedure with connection details?
why is the size of earth conductor is half of phase conductor.
1 Answers Century Pulp and Paper, L&T,
what is reactive poower
What does dny11 stand for?
arrange to send solved question and answer its easy to study and understand the thing, because of Exam is to be conducted shortly
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)