Answer / eduardo
In a delta connection you don´t have any access to the "mid
point" or if you prefer to the "neutral".
In a star connection you will have a four(th) terminal, that
you can connect to earth or use it as neutral conductor.
For example if you have a three phase power line at 15 kV,
and want 400 V and 230 V you can connect the primary in
delta (you don´t need the extra connection) and the
secondary at star. (delta- star)
Now you will have 400 V between any 2 phases and 230 V
between one phase and the star point of the transformer.
If you connect the secondary in delta you will not have 230
V, because you don´t have the 4th terminal. (delta-delta)
Please note that in star one winding of the transformer will
have 5,8 kV (10000V / sqrt(3)). In delta connection you will
have in one winding 10 kV. So verify the tension and the
connetction type of the transformer. (both primary and
secondary).
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / shahbaz shaikh
in delta-delta transformer primary side and secondary side of transformer are connected in delta fashion i,e R-Y-B are connected in triangle fashion these are generally prefer for the transmission system and here no neutral point is present and for the distribution system we use the delta star because our home appliances are work at 230v but in 3 phase we have 440v so to get the 230v we use delta primary and star secondary so by using one of phase and neutral point of star we can get the 230v.
| Is This Answer Correct ? | 0 Yes | 0 No |
when two gen set runing in parallel but thay have diffrent pole pitch, then what will be happan
what is the difference between ground and neutral?
what is there inside an inverter and how it works?
how can i change the rotation of the AC single phase induction motor and show me by diagram
One watt is equal to how many? we says one watt bulb,means what it consume?
How to calculate Air conditioning capacity for a telecom BTS shelter?
Can anyone explain, How will get positive to ground and negative to ground reference voltage in dc system
what is the diffrence between R Y B phase and why it is called RYB
If the maximum demand is 120 KVA in a building, then what is the Current taken according to load given ? Formula for it ?
why we step up voltage for reducing the loss, even if voltage and current are proportional anr resistance remains same
Briefly define and explain the following different types of Pulse Amplitude Modulation (PAM) with some examples. i) 2-PAM ii) 4-PAM iii) 8-PAM iv) 16-PAM v) Quadrature Amplitude Modulation (QAM)
Why ferranti effect occurred in leading p.f load?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)