STATOR EARTH FAULT PROTECTION :
Setting : 70% Time - 5 Sec.
Normally the generator stator neutral operates at a
potential close to ground. If a faulty phase winding
connected to ground, the normal low neutral voltage could
rise as high as line-to-neutral voltage depending on the
fault location. Although a single ground fault will not
necessarily cause immediate damage, the presence of one
increases the probability of a second. A second fault even
if detected by differential relay, may cause serious damage.
The usual method of detection fault is by measuring the
voltage across the secondary of neutral grounding
transformer (NGT). Here are two over lapping zones to detect
stator ground faults in a high impedance grounded generator
system, the two zones are put together cover 100% stator
winding for earth faults. A fundamental frequency neutral
over voltage relay covers about 0-95% of the stator zonal
winding for all faults except those near the neutral.
Another third harmonic neutral under voltage relay covers
remaining 96-100% of the stator zone 2 winding on neutral side.
Relays acted : a. Flag operation at Protection panel.
b. Acting of Master relay
c. Indication at Annunciation Panel.
Consequences : a. Tripping of 220KV breaker
b. Tripping of Field breaker
c. Stop command to Turbine thro’ Mark-IV
Status : a. Unit is at coasting down.


ROTOR EARTH FAULT PROTECTION (64R) :
Settings : Less than 80K ohm
Any rotor field winding of the generator is electrically
isolated from the ground. Therefore the existence of one
ground fault in the field winding will usually not damage
the rotor. However the presence of two or more ground faults
in the winding will cause magnetic and thermal imbalance
plus localized heating and damage to the rotor metallic
parts. The rotor earth fault may be caused due to insulation
failure of winding or inter-turn fault followed by localized
heat.
Relays acted : a. Flag operation at Protection panel.
b. Acting of Master relay
c. Indication at Annunciation Panel.
Consequences : a. Tripping of 220KV breaker
b. Tripping of Field breaker
c. Stop command to Turbine thro’ Mark-IV
Status : a. Unit is at coasting down.

Is This Answer Correct ?    2 Yes 4 No

Post New Answer

More Instrumentation Interview Questions

In a class of 150 students, 40 passed in Social Studies, 90 passed in Science and 30 failed in both the subjects. vi)How many students passed in at most one subject among Science and Social Science?

7 Answers   CAT, CGI, Cipla, KHK, Visa,


We have ZR22G-100-S-A-E-T-T--E-A/CV/F1 Model Zirconia Oxygen analyser which is Yokogawa make. I kept the analyser in Flue gas path at Air pre heater area. My plant is 7.5MW Biomass power plant. For a particular fuel, Coconut Husk which contains Sodium and Potassium chlorides iam not getting proper reading, Analyser output always Zero. I calibrated the analyser and it is OK. For Other fuels like Wood chips, Cholam waste, DOB, Groundnutshells, Ply wood waste and all iam getting actual percentage of Oxygen. What is the main reason behind this draw back?

2 Answers  


Which are all the commonly used Bordon tubes in the pressure gauges. Do any one use ASTM A 312 tubes for this purpose?

0 Answers  


explain how magnetic flowmeter works

1 Answers  


what is the meaning if the control valve CV is 27,in terms of selecting procedure?

2 Answers  






which type of signal used in instrument?

3 Answers   Emco, Makson, Sail, TATA,


installation process of orifice,a question asked for confusion creation in interview by BARC 1.if orifice is tightly fitted with pipe ,it will act like venturi 2.if orifice is left hanging in between liquid it will not create the pressure difference exactly,

0 Answers   BARC,


what is interface level measurement.who can calibrate interface level measurement transmitter online

0 Answers  


i want to find out iffco get test paper

2 Answers   IFFCO,


If hart communicator provide 4-20ma source to any transmitter during the callibration?

3 Answers   Hyundai,


Is there any interfacing sofware to build communication between a PC and ER300P model L&T make trivector meter via RS485 port which is available in the meter and is there any data acquisition card available to store the acquired data from the meter into the system

12 Answers  


Which standard is used for calibration of Control Valves ?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)