Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to test rotor &stator earth fault in turbine



how to test rotor &stator earth fault in turbine..

Answer / kannan

STATOR EARTH FAULT PROTECTION :
Setting : 70% Time - 5 Sec.
Normally the generator stator neutral operates at a
potential close to ground. If a faulty phase winding
connected to ground, the normal low neutral voltage could
rise as high as line-to-neutral voltage depending on the
fault location. Although a single ground fault will not
necessarily cause immediate damage, the presence of one
increases the probability of a second. A second fault even
if detected by differential relay, may cause serious damage.
The usual method of detection fault is by measuring the
voltage across the secondary of neutral grounding
transformer (NGT). Here are two over lapping zones to detect
stator ground faults in a high impedance grounded generator
system, the two zones are put together cover 100% stator
winding for earth faults. A fundamental frequency neutral
over voltage relay covers about 0-95% of the stator zonal
winding for all faults except those near the neutral.
Another third harmonic neutral under voltage relay covers
remaining 96-100% of the stator zone 2 winding on neutral side.
Relays acted : a. Flag operation at Protection panel.
b. Acting of Master relay
c. Indication at Annunciation Panel.
Consequences : a. Tripping of 220KV breaker
b. Tripping of Field breaker
c. Stop command to Turbine thro’ Mark-IV
Status : a. Unit is at coasting down.


ROTOR EARTH FAULT PROTECTION (64R) :
Settings : Less than 80K ohm
Any rotor field winding of the generator is electrically
isolated from the ground. Therefore the existence of one
ground fault in the field winding will usually not damage
the rotor. However the presence of two or more ground faults
in the winding will cause magnetic and thermal imbalance
plus localized heating and damage to the rotor metallic
parts. The rotor earth fault may be caused due to insulation
failure of winding or inter-turn fault followed by localized
heat.
Relays acted : a. Flag operation at Protection panel.
b. Acting of Master relay
c. Indication at Annunciation Panel.
Consequences : a. Tripping of 220KV breaker
b. Tripping of Field breaker
c. Stop command to Turbine thro’ Mark-IV
Status : a. Unit is at coasting down.

Is This Answer Correct ?    2 Yes 4 No

Post New Answer

More Instrumentation Interview Questions

flow transmitter range is 0 -500 mmwcc but the transmitter shows 12 ma for o mmwc instead of 4 ma ...how to solve this problem when we apply 375 mmwc it shows 16 ma

3 Answers  


Why Bently Nevada use negative voltage for vibration probes?

4 Answers  


what is HVAC?

1 Answers  


what is the zero elevation and zero supresstion in level measurement, how can use it?

2 Answers   GAIL,


what is written on orifice plate?

4 Answers  


why we r opening HOT BYPASS valve during startup of a compressor?

0 Answers   Hamsco,


why k factor is important to know in flow transmitter. if we don,t know k factor what will be issue we can face .

1 Answers   Flour Tech Engineers (P) Ltd,


What is critcal speed. what is resonant frequency. why we want to cross crtcal speed on higher RPM (early).

0 Answers  


Transmitter reading is zero but in DCS showing one Bar what is the reason ?

3 Answers  


centrifugal compressor interlock? Tell me the parameter at which compressor will trip

0 Answers   Cairn,


can u please give the exact ckt explaination of AC Drive related to industries.

6 Answers  


Q- Why Phase tester is only used for checking AC not DC ?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)