how we can measure the interface level?is it possible to
measure interface level with dp or pressure transmitter?
Answers were Sorted based on User's Feedback
Answer / m m chotrani
Yes we can measure interface level by purge method.you can
use two purges (sensors of ss pipe generally 1/4"NB).Now
for interface measurement two liquids of different
densities should be there. suppose the interphase takes
place between 300 and 450 mm height from the bottom of the
tank.now the interface be 50%. height difference (probe
distance is 150 mm. multiply 150 withe density of 1st
liquid say 0.8 gm/cc.which will be 120mm. and multiply 150
with the density of another liquid with the density say 1.2
gm/cc which is 180 mm.So your transmitter range is 120-180
mm of water column. calibrate the transmitter for this
range and connect both the probes to HP and LP connections
of transmitters
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ikarous
No,its not possible
you can use the level displacement transmitter which acts
according to buoyancy law
Is This Answer Correct ? | 2 Yes | 3 No |
what is three element in thermal boiler
what are the on/off valve precaution?
Which tank weighing system is better to install (Accuracy point of view) 1) Tank weighing system with 3 load cell or 2) Tank weighing system with 4 Load cell
GIVE THE TEMPERATURE RANGE OF PLATIUM RESISTANCE THERMOMETER.
I am applied 100 % pressure on to the air to open control valve,but the valve is not fully closed..and 10-15% is open the valve. how to calibrate the control valve?
if in a level tx height is given, how u calculate the ranges of the tx?
2 Answers Bombay Rayon Fashions, Invensys,
What is the Difference between CNC and PLC
what sud u do if u dont get feedback from control valve?
what is the difference between impact plate n coriolis type solid flow meters n how they works....n which one is better
What are the difference between mass flow meter, magnetic flow meter and vortex flow meter.
What is glanding
IF PLC POWER FAILURE THEN WHAT HAPPEN?