how we can measure the interface level?is it possible to
measure interface level with dp or pressure transmitter?
Answer Posted / m m chotrani
Yes we can measure interface level by purge method.you can
use two purges (sensors of ss pipe generally 1/4"NB).Now
for interface measurement two liquids of different
densities should be there. suppose the interphase takes
place between 300 and 450 mm height from the bottom of the
tank.now the interface be 50%. height difference (probe
distance is 150 mm. multiply 150 withe density of 1st
liquid say 0.8 gm/cc.which will be 120mm. and multiply 150
with the density of another liquid with the density say 1.2
gm/cc which is 180 mm.So your transmitter range is 120-180
mm of water column. calibrate the transmitter for this
range and connect both the probes to HP and LP connections
of transmitters
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
How does work A temperature valve or fv control valve in process plz brief me
whatis range of marcury filled tempereture gague
draw shematic diagram of c/v positioner(smart type)?
how can be calibrate flow indication transmitter (rosemount) it shows excess milli amps nearly about 24 ma on full scale, but its scale was set on 20ma on full scale..???how can be simiulate..???
What is Positive Calibration and Negative Calibration?
what is gas metering system? gas chromatograph? and gas compressors?
State four different types of flow measurement, for gas flow measurement MMSCFD is the common unit expand the unit and specify significance of word S in the unit.
give eg of how I/P is used in control loops
in sulfur process what is material of impulse line we use to connect with transmitter ? and does teflon affected by sulfur?
What is the PLC configuration in Cement industry?
how to tune siemens sipart electro pneumatic positioner..plz tel me..
in which principle pressure tx,level tx ,flow tx,temp tx ,control valve works?
How will you calibrate PID controller? explain with example.
How to calibration a control valve?
what should he know if he is an assitent engineer instrumentation in cement industries of experience of 10 - 15 year.