what's the reson that,Load is not same on VFD I/P and O/P
Side.whenever DOL condition load is same I/P and O/P side.
Answers were Sorted based on User's Feedback
Answer / prashant kumar sharma
Input frequency and Voltage at the VFD is constant but at
the output at the VFD is variable.
secondly the power factor at the Driven end is changing wrt
to load.
more over the Active and reactive part of Power is
deviating wrt to above factors thus the power at the input
and output of VFD are different.
in DOL none of the parameter like Voltage or Frequency are
changed thus Power remain same.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / shyam
in VFD, fist ac power rectify into dc power then convert it
into variable ac power.in this process energy loss as heat.
in DOL none of the parameter like Voltage or Frequency are
changed thus Power remain same.
| Is This Answer Correct ? | 0 Yes | 0 No |
If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , so what to do for solve this problem. The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?
What are the different types of temperature sensors and the principle they work on?
How to calibrate RC Feeder system in thermal power station?,If any instrument available to calibrate it,ple inform me. make:stock,
what is the difference between two wire transmitter and 4- wire transmitter
what is the usage of QDV & VOLUME BOOSTER
How can one improve linearity of an RTD based temperature measurement system?
What are primary elements of measuring pressure?
how can we measure the level measurement with the help of pressure gauge?
We have a Yokogawa Micro-XL DCS, which is having around 300 I/O, but whenever there is any wire gets grounded in field, the 24v supply to all loops gets dipped & all the indications at DCS goes to IOP(shows input open), at present we have fixed 500mA fuses in all the lines but which does not working. Does it required to replace with lower amps fuse, then how much or is there any other solution for this.
what is 24vdc live and dry supply
why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA?
For a diafhram 1.5 d =kn(p-p0) D4 Where d in deflection in inch k=constant n=no of capdule (P-P0)=Applied pressure in psi D In active dia at capsule. -1.5 d=k to p d being constant -1.5
0 Answers L&T, Shiv Tech Marine Control,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)