Answer / rahul sr
Passive Loop: The transducer must be provided by an
external power supply for its working. Then it generates
the signal according to the Process parameter. This may
have either 2 wires, 3 wires or 4 wires.
Active Loop: There is no need to give external power supply
for the transducer. The sensor itself generates signal
without giving power supply. This will have only 2 wires.
| Is This Answer Correct ? | 40 Yes | 22 No |
Answer / anatoli
Active input - loop is powered from card/module
Passive input - loop is powered from external source
Output loops are always active.
Number of wires is irrelevant
| Is This Answer Correct ? | 13 Yes | 2 No |
Answer / ali
Kindly check the data sheet of Stahl Transmitter Supply Unit
Field Circuit Ex i
Series 9160
and check 9160/13-10-11 as passive O/P & 9160/13-11-11 as active O/P .
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ali
If we consider temperature sensors for example , active sensors are like LM35 -3 wires, need supply - thermocouples 2 wires -don't need supply , but both of them give mV as O/P .
on other hand pt100 can't gives O/P voltage or current with or without supply .
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / ram
Passive Loop : Two wired loop powered . It is consuming the
power and generates the signal acoording to the process
parameter values or inputs.
Active Loop : External Power supply or separate power
supply and Signals generates either two wire or four wire
concept.
| Is This Answer Correct ? | 11 Yes | 13 No |
for oil & gas industries which zone is normally preferred? why? give its example?
Boiler flame scanner working principle?
what is the difference between dcs & plc
Why grounding is necessary? Give example with diagram.
0 Answers Bright Point, DS Group,
can i use capillary type dp transmitter converted to capillary type pressure transmitter. if i removed one side capillary tube its work correctly?
Hot calibrate a level transmitter (wet & dry legs)?
what is mass flow meter, working principle of mass flow meter and its installation.
if temperature transmitter is showing wran. sensor 2 fail how can you remove from the transmitter display m/n.3144p rosemount
A valve in series with an orifice plate (DP transmitter), is aligned for constant pressure in the pipeline, if there is an error dx, How to align it in process.
My flow transmitter range is 0-1000mmwc.DCS range is 0- 100m3/hr.What is correspond out put in terms of milliamps if my flow is 65m3/hr
what is o2 analyzer and how it measured ,what is the role of this analyzer in cfbc boiler...
how to calibrate displacer type level transmitter by dry weight method please mention formula for weight calculation
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)