in the boiler in the main steam line and its bypass line and
the startup vent vales are only motorised valves why cant we
use other types of valves such as pneumatic.
Answers were Sorted based on User's Feedback
The design engineers must have had a reason why they
selected to use motorized valves in stead of pneumatic
valves. It might be that they felt the main power is less
likely to fall away than the plant air compressor tripping
and there is no air to operate these valves. It also
sometimes happens that the main instrumentation supply UPS
(24VDC) will trip and the whole plant looses the
instrumentation supply but the main supply is still available.
Also if the main power do fall away there is always the
emergency generators that will kick in and supply emergency
main supply to all the critical systems.
Just for interest they tend to select motorized valves for
safety systems as well like foam, fire pump control valves
and deluge main control valves, most probably for the same
reasons.
Good luck
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / rajender
For Very high Pressure Applications motorised valves are
used.
| Is This Answer Correct ? | 1 Yes | 2 No |
waht is difference between pressure transmitter and transuducer
What is full form of hart communicator?
WHY WE NOT USE 2-20mA,1-20mA,3-20mA or 10-50mA SIGNAL? INSTEAD OF 4-20mA.
6 Answers Hindustan Unilever Limited, Yashmun Engineers,
What is derating factor in Motor?
what is difference between total flow and flow rate in general ?? explain it with daily life example.
why we r opening HOT BYPASS valve during startup of a compressor?
Please any one can explain how to calibrate transmitter (smart) online with out remove from the container suppose it is interface level or static pressure level measurement we dont want to remove transmitter from the container mean it is running plant please give me detail. thankx brothers
what is the difference between RTU & MTU in SCADA system?
how feedback signal frm rtd can be use for 2 purpose, i.e. 1for local monitoring and 2nd for controlling in dcs.so how many wired RTD can be used
given a processor batch of 1000 resistors moving on the conveyor belting in a large factory. the resistors is value at 10k ohms each but when the resistors reach the quality control, some of the resistor has been rejected caused by failure in manufacturing.the high quality measurement is used to determine the failure. describe the instrumentation terminology in measurement of a system above with explaining the important in:- -reliability -sensitivity -repeatability -precision -range -resolution -linearity -hysteresis -error -accuracy (answer must related to the scenario above)
If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used? Please tell me its Calculation formula.
why we use 250 ohms across HART CALIBRATOR DURING CALIBRATION OF TRANSMITTER
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)