why the admittance matrix or y bus matrix of a large network
is called sparse matrix?
Answers were Sorted based on User's Feedback
Answer / iamdon
In case of large network there are 1000(e.g) busbars,one
busbar is connnected to adjacent busbars whose numbers are
very less(e.g 6-10) as compared to the total no buses in
network.So when the Y matrix is formed, most of the
elements of Y becomes 0.Zero values of Y are for such
elements between two buses which are not physically
connected.
The term sparse indicate the same fact that,very few
elements of Y matrix are nonzero.Thats why Y matrix is
called sparse matrix.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 45 Yes | 1 No |
Answer / parth bhatt(b.e)
In the admittance matrix, each non-zero diagonal element corresponds to network branch connecting the pair of buses indicated by the row and column of the element.
In most transmission network, most of the off diagonal elements are zero. So the admittance matrix are relatively zero.
| Is This Answer Correct ? | 8 Yes | 5 No |
Answer / bharat rathod
> Y-bus and Z-bus both are used for designing and modeling of transmission system.
> Removal of short-circuit element is easy in case of Z-bus. And any modification in Z-bus is easy. Z-bus is always full matrix.
> Any modification like removal of any transmission line is difficult in case of Y-bus. And, Y-bus is highly sparse. Y-bus is having 97% sparcity.
| Is This Answer Correct ? | 1 Yes | 3 No |
Safety of dry type transformer
what does kirlosker deals with?
how much power consumed by 1.5 ton capacity split A.C in 1 hour
why designer use kva rating instead of kw in transformer rating???????????????
what r the tests on the 3 phase transformers can any one explain how to test using megger on transformers thx
IN THE CASE OF AN ELCB, IF THERE IS ANY UNSTABILITY BETWEEN PHASE AND NEUTRAL IT MAY TRIP. BUT MY QUESTION IS WHEN A LOAD IS CONNECTED IN BETWEEN P AND N, THE LOAD CONSUMES SOME POWER AND THERE IS A DIFFERENCE IN NEUTRAL WITH RESPECT TO THE PHASE. THUS ACCORDING TO ME, THE ELCB WILL AUTOMATICALLY OPERATES WHEN EVER THE LOAD CONSUMES-- I KNOW IT IS WRONG. BUT THE SOLUTION IS?????????
What is the Derating factor of power cables when exposed to direct sunlight in (both PVC & XLPE).
Differance between ELCB and RCCB?
what is meant by HT<?
Which generation plant has instant start
is 3-phase induction motor need a starter ? why do it so
I have 150/1A Rating CT Suppose if i inject 15A in CT " Secondary" means what will happen ??????
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)