why transformer are rated in KVA not in watt?
Answers were Sorted based on User's Feedback
Answer / ramaraj.g
the cu loss of the transformer depends on current and iron
loss on the voltages .so total transformer loss depends on
volt- amps (VA)and NOT on phase angle between voltages and
current it is independent of the load factor. That is the
rating of transformer is in KVA /VA and NOT in KW/Watts
Is This Answer Correct ? | 77 Yes | 9 No |
Answer / c_elavarasi@yahoo.com
we know,real power P=VIcos@ ,which is represented in KW.
the apparent power S=VI ,which is represented in KVA. so if
we wish to represent the rating in watt,we need the power
factor value.the power factor of the load is not known when
the transformer is manufactured,so we represent rating in
KVA as it is in no need of power factor
Is This Answer Correct ? | 44 Yes | 16 No |
Answer / syed qamar abbas
There are two types of losses in transformer. One is
variable type i.e. copper loss which depends on load
current since load current is of variable nature thats why
it is called varialbe losses and the other is fixed or
constant losses i.e iron loss which depends on voltage and
frequency,since both voltage and frequency is fixed that is
why it is called constant or fixed type of losses. These
two types of losses are not affected by the power factor.
This is why transformers are rated in KVA and not KW
Is This Answer Correct ? | 19 Yes | 6 No |
Answer / adeed khan
all loses in transformer depends on the current and voltage for this we can say transformer rating can measure in kw instead of KVA
Is This Answer Correct ? | 0 Yes | 1 No |
As we know the load power factor is unknown for the every
transformer, we take its rating in KVA = V.I.Cos.ф. so that
whatever would be the power factor, can be taken to
calculate the load.
Is This Answer Correct ? | 2 Yes | 7 No |
Answer / karthik_elec
KVA*p.f = KW, the power factor is depaending upon the load, what load we going to give we dont know, thats y transformers normaly rated in KVA, but for testing purpose we can assume p.f is 0.8 ( induction machine average p.f)
Is This Answer Correct ? | 1 Yes | 8 No |
Answer / gurwinder
because the current is very high.when the current is high
then it is measured by volts.
Is This Answer Correct ? | 1 Yes | 8 No |
What is AMF Panel????
Which are resistive loads & which one are inductive loads : Refrigerator, Split air conditioner, ceiling fans, well pump, fluoresecent bulbs, T.V, CRT Monitors, Adsl Routers, C.P.U, Printers, Deep Freezers, Speakers, DVD Players, Microwave oven etc. ? Output Power for these Appliances Would be same like this : P = V * A * P.F Or would be changed ? thanks
This is reqd for a 1MW Solar power plant..We have 2DC outputs from the solar panels Connected to 2INVERTOR panels.. Output from invertor is 3ph,280v,500kva,50hz.These are connected to individual ACB.This has to be stepped up to 11KV ,1250KVA SYSTEM.Now can I use (1) one more ACBTO GIVE A COMBINED OUTPUT OF 1000KVA,280V & STEP UP THE OUTPUT BY USING a single two winding 3 ph transformer 11kv/1250kva. or (2)use the two outputs and connect to one three winding transformer of above rating..Pls suggestwith details.
I have a drawing of a wound rotor induction motor for a crane. This crane motor has 5 forward speeds & 5 reverse speed implemented of course with different amount of resistance for each speed setting selected. What has got me scratching around is the fact that 8 of the 10 speed selections switch in uneven (unbalanced) amounts of resistances on each of the 3 connections to the motor's rotor.Can this be possible? I would have assumed this would produce unbalanced rotor currents and therefore vibration in the motor. I would greatly appreciate anyone's comments on this. Many thanks, Confused.
why earth wire is needed in a wiring system
in ONAN type transformer winding temperature is lower than oil temperature at evening time but morning winding temp is higher than oil temp what is the reason?
How we detect the leakage current of 11 KV H.T. motors and waht is the maximim limit?
1.what is bus cuplour and main funtions. 2.what is main function of alternator. 3.how many types of dg oils.
what is XF 200/240 V AC for Drawout Breaker.
How will be the single line diagram of series trip HT breaker? how it works?
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?
how does directional relay work incase of ac ?