How can we check Zero of DP type Level Transmitter onside?..

Answer / vijay

close the hp and lp valve and drain the water then open the
vent valve it should show the zero value.

Is This Answer Correct ?    14 Yes 6 No

How can we check Zero of DP type Level Transmitter onside?..

Answer / altamash

close the both valve ie LP & HP then drain the water and then open the vent of LP then connect the HART and do the zero trim by HART then we can find ZERO

Is This Answer Correct ?    6 Yes 2 No

How can we check Zero of DP type Level Transmitter onside?..

Answer / jayaram

1.close the both HP and LP rootvalves
2.open the both HP and LP drain valves to drain the service
completely.
3.Close the drain valves.
4.open the vent caps of both HP and LP leadlines near the
rootvalves.
5.fill the lead lines completely with water.
6.obviously LP side , more pressure acts and current goes
below 4mA. So elevate the Zero Potentiometer to 4 mA(this
is for analog standard dp transmitter).
7.first of all you have to calibrate the dp transmitter for
the required range, then only you can do this elevation
zero checking.

Is This Answer Correct ?    11 Yes 8 No




How can we check Zero of DP type Level Transmitter onside?..

Answer / vishal

Just open the equilizer valve and u will get zero
No need to open or close any other valve
Check by multimeter

Is This Answer Correct ?    3 Yes 1 No

How can we check Zero of DP type Level Transmitter onside?..

Answer / suresh agravat,jamnagar

first close the rootvalve then drain trhough needle velve
then close both LP and HP isolated valve and open equliser
valve

Is This Answer Correct ?    3 Yes 4 No

How can we check Zero of DP type Level Transmitter onside?..

Answer / muhammad yasir

close HP isolation valve open HP side drain valve.Transimiter read maximum Differential pressure and Transimiter show O% Level or 4ma because LP lmpluse line liqued act pressure on LP side Transimiter.
When span check close both HP and LP side valves and open drain valve Transimiter read 0 differential pressure.Transimitter show 100% level or 20ma.

Is This Answer Correct ?    1 Yes 2 No

How can we check Zero of DP type Level Transmitter onside?..

Answer / faiyaz ahmad

first open the equalizing and then close the isolation valve and open the vent valve both side and make it zero in this condition transmitter will show zero.

Is This Answer Correct ?    0 Yes 2 No

Post New Answer



More Instrumentation Interview Questions

can any one pl explain me in brief that how we select the leakage classification in valve,means for liquid or gas there is any standard for selecting leakage classification or its depend upon valve size or any any other parameter.

3 Answers  


why we require Differential pressure?Why we use Orifice Plate?

3 Answers  


what5 does intrinsically safe mean.

2 Answers  


Single acting ON-OFF valve. it is air to open. when sov energized , valve will be open, so during that if air fail then what will be the condition of valve ( open or close ) ???

4 Answers  


How to check vortex flow meter is in good condition while we do not having calibration setup?

4 Answers  






Hi i m B.E. In elect. & comm. I m workin in bio mass plant from 6 mnths as inst. Engg. but now i m in dept. Of operation as shift engg...which is best operation or inst. 4 me? M confusd..plz help and reply me..

2 Answers  


In control valves (like feed water control valve) we will give 3 kg pressure and how it controls 110 kg of water pressure?

4 Answers   SSL,


How do you calibration D.P transmitter? ?

2 Answers   Power Plant,


Explain about the leakage class of the control valves

0 Answers   CCIE,


uses of profibus?

1 Answers  


I have energy meter for educational project having 0.5s class but my friend need 0.2s class meter , which one is good for that purpose and what is the actual difference of that two classes , need very easy example also.??

0 Answers   BBS,


You are looking at the RS-485-side of an RS-232/RS-485 converter and the power supply voltage for the converter is +5V. Under idle conditions (no transmission), and assuming you have enabled the RS-485 output: what would you expect at: (a) Output A measured against output B (b) Output A measured against ground (c) Output B measured against ground

1 Answers   EIT,






Categories
  • Civil Engineering Interview Questions Civil Engineering (5069)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4437)
  • Electrical Engineering Interview Questions Electrical Engineering (16573)
  • Electronics Communications Interview Questions Electronics Communications (3915)
  • Chemical Engineering Interview Questions Chemical Engineering (1091)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (214)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (258)
  • Instrumentation Interview Questions Instrumentation (2984)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (96)
  • Marine Engineering Interview Questions Marine Engineering (122)
  • Power Plant Engineering Interview Questions Power Plant Engineering (170)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (0)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1376)