what is the difference b/w circuit breakers and relays?
Answers were Sorted based on User's Feedback
Answer / inderpal
Circuit Breaker is a protection device which can intrupt
the fault current, CB has high fault level with-stand
capacity (kA). Relays are also used in protection circuit
but relays cannot with-stand high fault levels. Relays are
generally used as sensing element to open the circuit
breakers.
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / karthik
relay is used only to sense the fault in the system....
whereas, circuit breaker will trip the circuit as soon as
relay sense the fault and sends the signal to the circuit
breaker.............. the fault is identified and it also
trips the system.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / chetan
Relay is simply a sensing device which sense the fault condition as per its setting and give information to circuit breaker to break the circuit or take the required action
where as circuit breaker is a protecting device which immediately trip the circuit when a fault condition occur or when it get a faulted signal from relay
| Is This Answer Correct ? | 3 Yes | 0 No |
Will MCB tripped off, if there is an electric shock to Human body?
which is the best, A/C DRIVES or D/C DRIVES for cranes,...... ...and why......?
what is "pu" in electrical engg.
On PVC conduit the class "A" "B" or "C" is marked what does it shows. Either its thickness or its composition?
Shunt reactor is used in EHV Transmission line for..............?
Why positive terminal of DC 48V was earthed?
What is the meaning of burden and class of accuracy of CT?
Why reactive power is needed in a power system? How is it being absorbed or delivered by alternators? For reactive power control we are changing excitation but reactive power absorbing or delivering related to stator. How these two are interlinked? i want a detailed explanation with necessary expressions and figures?
which fault is severe and why?between lll fault and lllg fault which fault is severe and y?
What kind of preventive maintenance are there for transformer?
if 400kv line is connected to the load but neutral ii not be connceted then wt ll happen
I HAVE A INCOMING 100A MCCB TPN 25KA, CABLE LENGHT OF 80M 70MM CABLE SIZE FROM MAIN SUBBOARD TO NEW DB.BASE ON THE FAULT LEVEL SETTING OF 45KA.I WOULD LIKE TO FIND OUT 25KA ENOUGH KA. APPRECIATE IF SOMEBODY CAN ASSIST ME WITH FORMULA FOR THIS. FRM: JEFF
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)