Initially motor starts with star connection ,after few
timing changes to delta connection, why the motor should
run continously in star connection,it gives high torque &
low current?
Answers were Sorted based on User's Feedback
Answer / madhu
basically in star connection line current is equal to phase
current,it gives high starting torque. after motor reaches
pick up speed we changed to delta.because in delta line
voltage is equal to phase voltage& line current is root 3
times the phase current.if we run in star in running time
the power losses are more due to current is high. thats why
we changed star to delta.
| Is This Answer Correct ? | 18 Yes | 3 No |
The purpose of starter is to start the motor and to limit
the starting current.we are starting the motor in y-
connetion during this impedence of two windings put across
the line voltage hence the starting current gettinh
redeuced
but the motor rated capacity (out put torque)can only be
obtained when itis changed to delta connection this time
the voltage is incresed bu 1.732 time to meet the torque
(torque is direct proportion to square of supply voltage .
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / velusamy
There are two reasons
1.To get high starting torque, motor runs at star for
predetermined duration and then changed to delta.
2.If the motor runs continuously , the capacity of the
motor is reduced by root 3 times (Capacity of motor
rating/1.7324) and hence motor will fail if the OL setting
is not reduced to 1.7324times of motor full load current).
| Is This Answer Correct ? | 6 Yes | 2 No |
Reason of secondary of ct always short
what is meant by VFD ?where its useful ?
what is the difference between indoor package substation and outdoor
what will be the effect if you were using different brands of outlets?
wat is syncronization . wat parameter will take for syncronization.
what is the pre commissioning test to be carried out on LT power panel at site?
if earthing is used in place of neutral how the circuit completd.
why is corona loss greater in a stranded conductor as compared to a solid conductor ?
What happened when voltage will half value of current ...
we all know that in transformer, voltage and current are inversely related i.e. Vp/Vs= Is/Ip....so in standard CT..we have a ratio of 200/5...that means our voltage should increase by ratio of 40..althoug that is not the case...because that requires high insulation level.and pratically not feasible......can anybody clarify my ques.......thanx
why the rotor is outside in case of ceiling fan?
armature winding of dc machine produce alternating emf then it convert in to dc by using commutator.But only we consider armature resistance why don't we consider inductive reactane effect?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)