I HAVE A 1 MVA TRANSFORMER, I WANT TO KNOW THE FAULT LEVEL OF
THE SYSTEM ( WHAT IS FAULT LEVEL PLEASE EXPLAIN WITH EXAMPLE)
Answers were Sorted based on User's Feedback
FAULT LEVEL MEANS SHORT CIRCUIT CAPACITY OF TRANSFORMER.YOU
HAVE NOT MENTIONED THE VALUE OF TRANSFORMER RATIO & % OF
IMPEDENCE.ASSUMED VOLTAGE RATIO= 11KV/415 V & % OF
IMPEDENCE=6%.
RATED FULL LOAD AMP OUTPUT =1MVA/(415 X 1.732)=1391.25A
SO SHORT CIRCUIT CAPACITY OF TRANSFORMER= 1391.25/6%
=23187.44 A
IF ANY FAULT OCCURED THEN THE ABOVE TRANSFORMER WITHSTAND
THE SHORT CIRCUIT CURRENT OF 23187 A.
| Is This Answer Correct ? | 33 Yes | 4 No |
1 MVA, 11/0.415kV Transformer
Full load current= 1000000/(1.732x415) = 1391.24A
% Z(Impedance)=5 (As per IS 2026 for transformer ratings of
0.631 MVA to 1.24 MVA)
Fault current= IFL/%Z =1391.24/0.05 =27.824 kA
| Is This Answer Correct ? | 18 Yes | 3 No |
Answer / raj l. lahare
For correct Fault level the DATA given is not sufficient. You need to give the Voltage Ratio and the % impedance of the Transformer.
| Is This Answer Correct ? | 1 Yes | 0 No |
How do you calculate of power factor, if it is lagging or leading for unit(1).
If one d.g. is unable to take full load of system, then second d.g. will take care of partly Load.for this condition RPM of both DG set should be equal.By using Synchronization panel RPM of dg sets are match, is it true?
If Two Generators are working parellel in a network and suddenly the field of one Generator get weakened What will happened if there is no reverse power relay fixed in that Generator panel????
why the earth terminal in three pin top is longer than rest of the two terminal and of bigger size?
what is suitable alternative for an igbt?
what is the voltages using in movie theaters??? why ??why not other??
What are the different protection systems takes place on control panel board?
How to run a three phase motor into single phase........
As per IS why should the control be taken only from R phase, why not from B or Y phase??!!
why capacitor bank is not used in generator power
If i have two 3000 kW motors and the whole facility requires a 10 MVA transformer. What would be better installing two 5 MVA transformers(one for 1 motor ) or just a single 10 MVA transformer for both of them. Give reasons for your answer.
flurescent bulb rating is to 230v,50HZ.now flurescent connected 230v,25HZ.whether nreduced frequency will affect the glowing properties of flurescent.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)