why capacitor bank is not used in generator power
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
When the generators(gen) are connected to grid or net work
,if all the gens are run at unity pf ,there will be drop in
voltage due to inductive load in the system as the current
increases.Then to maintain system stability, LDC requests
large generating stations to increase the voltage . This
will increase the KVAR and results in lower lagging pf in
the gens. That is why the gens are designed for 0.8/0.85
pf.The pf of gens can be kept at any value by varying
excitation or resetting in APF mode.As pf control is
required by generating stations,capacitor banks are not used
.Capacitor banks can be used in the system to reduce the
inductive load but not in the gen stations.
Is This Answer Correct ? | 18 Yes | 1 No |
Answer / k.prakashchandra
Pf of generator can be brought to required value by varying
excitation.
Is This Answer Correct ? | 12 Yes | 3 No |
Answer / k.prakashchandra
If the gen is connected to grid ,its pf can be regulated by
varying the excitation or by APF mode.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / umkesh
One more question can be use Capacitor Bank in Aux consumption panels in Thermal Power plant like CHP
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
In the line 9, read as ' As pf control is not required'.
Is This Answer Correct ? | 1 Yes | 4 No |
Why only mesh earthing is used in G.S.S.?
why circuit breaker closing time is always higher then tripping / opening time.
how to failure indution motor insulation & how to improve heat in motor insulation
0 Answers BHL, EPIL, IFFCO, Micromax,
why do we prefer a 3-phase delta connected load rather than star connected?
How can transformer winding insulation be measured (Delta & Star Connections)?
What are the effects of electrical faults?
what is apparent poewr, reactive power, & active power?
what will be efficient rating of ac motor to lift a 10 kg wt of stone to 10 meter height with input 220V AC 50 Hz frequency???
33kv Rated output avilable in market (any where in india)
What is mean by ideal infinite bus? Why it is required to consider in fault short circuit calculations?
what is ideal insulator. what are its parameter. Is poecelain insulator comes under this category.
why high current produce in case of transformer when turns are internally gets shorted.