How big (size) can the tertiary winding be in transformer?
Can we load the tertiary winding, if yes then how much we
can load it?
Answer / rabramovitz
Tyically for stabilizing an oscillating neutral, about 35%
of the KVA (or VA) supplied. Yes, it can be loaded, as long
as you don't exceed the current rating for its gage (do not
exceed current which causes a temp rise at or below the
class of the transformer). The current capability (if
properly designed)will be about a third of a primary phase
current normalized to the tertiary ratio. (call it NI/3)on
a per phase basis.
Is This Answer Correct ? | 0 Yes | 0 No |
1)What will you do if main incomer VCB fail in your site ?
is that a problem if i connect a single phase load to a secondry delta connected transformer but i get a neutral from other transformer i the system?
how many amps in 1KVA?
How to check 11000/1.732 to 110/1.732 Potentila transformer (PT)?
what is formula of illumation calculation
How to Make relay co ordination chart for a Electrical power distribution of a plant
what will happen if any motor runs long time with star connection in400vA.C. system
what is Basic Engineering.,FEED and Detail Engineering with respect to Electrical Engineering.(Explain with Example)
what is function of capacitor in ceiling fan?
describe the Operation of induction generators from bus bars
how to calculate KA rating of C.B?explain with Formula.
When we have earthing mesh or underground earthing network in industrial plants, weather we have NT-S or NT-C-S kind of earthing system, so eventually weather we must use 4 or 5 wire in 400 volt level (For example 3×150+70 mm2 or 5×150 mm2) in this connection I would like to know exactly the paragraph of IEC or IEEE number