Assume a condition such that two motors of rating
6.6kv,415v are connected to blower,so tell me which motor
draw large current give appropriate reason?
Answers were Sorted based on User's Feedback
Answer / pillay
The current drawn depends on the power consumed by the motor
and the operating voltage.
KW =1.72 X VL X IL X PF
Now assuming both the motors are loaded at 100 kw each OF PF
0.8 than the 6.6kv motors current consumption will be
100000KW /1.72 X 6600 X 0.8 =11 AMPS
If 415 volts is used than
100000 / 1.72 x 415 x 0.8 = 175 AMPS.
Is This Answer Correct ? | 17 Yes | 1 No |
A 2083kva AVR was tested, phase to ground shows continuity, what is the implications
Why we used 690V in ACS 800 drives.Why dont use standard voltage like 415v or 1.1Kv
How to calcluate the current by means wires/cables in square mm
what is the easiest method of short circuit current calculation ? pls. derive with a mathematical example in real life application.
what is the difference between ac and electric
What is pole slipping relay? When it is operated?
what is the effect of back reactive power on the generator ?
For overhead protection we use which transformer?
what is slip?
Hello everyone, somebody knows what is a "surplice power" ? The hole phrase is: "This rating is appropriate for a generator set paralleled with an infinite bus e.g. a national electrical supply network or grid where the generator set is run at 100% load, 24 hours a day, 365 days a year and any surplice power is exported into the grid" Thanks in advance.