Answer / neeladree chakravorty
Yes we can .
In fact if we use higher frequency then according to the emf
relation of E=4.44fBAN,
we can see that for a given rated voltage, the Area of cross
section of the transformer core will reduce.
So the Volume of the transformer will be reduced and hence
it will be lighter and lower will be the material cost.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / nagarjuna
i cant understand u r answer NEELADREE.WIL U TEL ME CAN WE USE R NOT,IF S HOW.IF NO Y.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / neeladree
Nagarjuna,
I had mentioned my answer in the first line. "Yes we can".
the reason is clearly mentioned.
But mind it, that the transformer is designed for 70 Hz
operation and we are operating it at 70 Hz.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / nithi
yes. we can use the transformer for 70 Hz with same voltage
rating.
Reason: For the same voltage rating if we increase the
frequency,the flux carried by the core material will be
reduced .Thereby the hysteresis loss is reduced which
results, reduced iron loss.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kc
a transformer can be operated at 70 hz but the kva and emf rating increases; also the lines connected to it should be capable of changing the freq at its entry and exit pts to synchronise with the line freq of 50 hz in india and 60 hz in the usa.also with higher freq the area of cross section of laminations decr which makes it diff and costly to manufacture.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / arun
YES WE CAN IN FACT ON HIGHER FREQUENCY THE LOSSES WILL DECREASES AS Ph=Kh *f*Bmax1.6* (hystereis loss )
Pe=Ke*f2*Bmax2(eddy current loss)
V=4.44*f*Bmax*N
so if i put the value of Bmax from the third equetion then eddy curren loss will be independent of the frequency but hysterysis loss is inverly propotional to B(power .6 )
so from here its clear that if frequencuy increase then losses decreases so
| Is This Answer Correct ? | 0 Yes | 1 No |
what is mean by kneepoint voltage? when it will happen? ( my doubt is, if CT secondary is open means ct get saturation or blas? what are factors are required for calculations? plz give currect anws:
What is the formula to calculate the rating of power cable for three phase current.
high voltage transformer input voltage,current and amps rating..distributed transformer input voltage,current and amps rating...
Between Star-Delta & Star-Star Power transformer which one is efficent for Earth Fault?
What is the function of mid point voltage in battery bank
1 Answers Jindal Steel and Power,
how to set the time in digital timer ?
what is the purpose of bypass mode in energy lighting transformer?
what is the role of energy meter in distribution system ???? technical and non technical losses in distribution system????
what is the funtion of conservator in transformers?
How amny AH battery required for 600va inverter ?And how many hours it will give backup for ceiling fan ?
CTs Ratio
In case of 3Phase Supply, Voltage R-Earth/Neutral - 220 Y-Earth/Neutral - 220 Z-Earth/Neutral - 220 Total is -> 660Volts Then Why it is said that 3Phase supply is 440
6 Answers Hindustan Unilever Limited,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)