How will you design a capacitor bank for a plant? if my p.f
is 0.6 i have to improve it to 0.9 or 1 what kind of steps i
have to do? and is there any formula for calculating this?
Answers were Sorted based on User's Feedback
Answer / joel q.
You must add a capacitor bank. you can determine the size
of the capacitor to be added using the following formula.
KVAR = KW*Tan((arccos0.6) -(Arccos0.9))
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / raju
to improve powerfactor only capacitor banks should be used
but not inductor as capacitor having leading pf which wil
reduces reactive power and improves pf
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / kaushik
if we are talking for 0.6 pf laging to 1 pf then we require
a capacitor bank.
the rating of the bank will be=v*i*sin(angle) in vars
angle=cosinverse(0.6).
if we are talking for 0.6 pf leading to 1 pf then we require
a inductor bank.
the rating of the bank will be=v*i*sin(angle) in vars
angle=cosinverse(0.6).
v=supply line voltage.
i=line current.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amrish sharma
just calculate total load of plant,,, then use capacitor 30
percent rating of total load,,, example if you have hunderd
ampere load then use 30Kvar capacitor,,,
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / saravanakumar
If you want improve your power factor, you should provide a
capacitor bank.The rating of the bank is 1/3 rd of the
transformer ratings.
| Is This Answer Correct ? | 1 Yes | 4 No |
what is ballast
Why 9KV surge arrester having 7.65KV of MCOV?
explain working principle of earth leakage relay
0 Answers Divis Laboratories, SMIORE,
what is the difference between dropout fuse and horn gap fuse. how to choose between them
how to commissioning the genset with amf panel?
In a power system we know that if the generated power is less than the load then the frequency of the system is decreases.So does this mean that total required load is delivered at alower frequency?
Interchange 7 and 6 ,÷and× 36×7+4-7×3
What is meant by positive and negative feedback?
how moving coil indicator works?
What are the protection required for Transformer, motor, Line, Generator, capacitor, that all i have to refer which standard?(Like Transformer detail IS 2026)
state basic meaning of 'INDUSTIAL AUTOMATION'?
why single phase to grd test in HV cable?why not 2 phase at a time?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)