When i went to a interview the interviewer ask me a
question for that i cant able to answer him if anyone knows
answer me
How will you design a capacitor bank for a plant? if my p.f
is 0.6 i have to improve it to 0.9 or 1 what kind of steps i
have to do? and is there any formula for calculating this?
Answers were Sorted based on User's Feedback
Answer / joel q.
You must add a capacitor bank. you can determine the size
of the capacitor to be added using the following formula.
KVAR = KW*Tan((arccos0.6) -(Arccos0.9))
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / raju
to improve powerfactor only capacitor banks should be used
but not inductor as capacitor having leading pf which wil
reduces reactive power and improves pf
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / kaushik
if we are talking for 0.6 pf laging to 1 pf then we require
a capacitor bank.
the rating of the bank will be=v*i*sin(angle) in vars
angle=cosinverse(0.6).
if we are talking for 0.6 pf leading to 1 pf then we require
a inductor bank.
the rating of the bank will be=v*i*sin(angle) in vars
angle=cosinverse(0.6).
v=supply line voltage.
i=line current.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amrish sharma
just calculate total load of plant,,, then use capacitor 30
percent rating of total load,,, example if you have hunderd
ampere load then use 30Kvar capacitor,,,
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / saravanakumar
If you want improve your power factor, you should provide a
capacitor bank.The rating of the bank is 1/3 rd of the
transformer ratings.
Is This Answer Correct ? | 1 Yes | 4 No |
why phase & neutral is use in tv? why earthing not use ?
what is the difference between 'Control Transformer & Potential/Voltage Transformer'?
Generator,motor and alternator Working principal Please explain easily
How to calculate the value of earth capacitance in a transmission line.
Sir, I have applied for the of Jr.engineer(Electrical & Electronics) & ASST. LOCO PILOT at ALL RRB BOARDS. please send me all RRB Boards solved papers in the year of 2001 tO till date. i requested send me the papers to my id as soon as possible (jet_0991@yahoo.com). (This is very urgent) Thank You,
what is the voltage regulation for unity and zero power factor?
When a capcitor is used on 440 v thenthis is kvar rating 25kvar .my question is that when we use this capcitor use 480 v &525 volt .how much kvar increase . Plz give my question ans. And give answer with formula .my mail id is rohitashsaini013@gmail.com
do you know measure the earth resistance?explain
what is the function of commutator in dc motor?
52 Answers Aviation, HP, Raj Construction, TCE, University Exams,
How would you supply power to a village which is very far from a sub-station and has only a 11kV line running near by?
Please let me know when replacing electromechanical Relays for protection of generators with sr489 multilin Relay, then there is no need to use 86 master trip relay Too. I am wondering this multilin relay has no contact to Stop breaker reclosing as 86 does
IT IS SAID THAT THE OLTC OPERATION SHOULD NOT BE PERFORMED WHEN THE TRANSFORMER IS GENERATION TRANSFOREMR/STEP UP MODE. WHY IS IT SO?
1 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,