Why we use Y-Y connection in power transformer (8-10 MVA,
132 kV to 11 KV)and D-y in distribution transformer (2 MVA,
11 KV to 440 Volts)?
Answers were Sorted based on User's Feedback
Answer / rajesh kumar
we use y-y conection in exctra high voltage transformer
like 132kv as we know that in star connection line voltage
is-1.732.phase voltage.so less insulation required in y-y
conection.
in distrubution transformer at 11kv we can easily insulate
windings due to voltage level is low.and also get domestic
load.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / rajesh kumar
we use y-y connection in power transformer 132kv as we know
that in star connection line voltage is-1.732.phase
voltage.so it is easy to insulate the winding as the
voltage level is low.and cost is less due to degrading of
insulation.
| Is This Answer Correct ? | 3 Yes | 0 No |
ok u r using any transformer , anywhere but
the important is what is ur need ?
if u want , in distribution u need 440v -phase to neutral
u r using star connection
u need 11kv hv , u use delta connection
the important is u r using neutral or not generally line
side transformer has delta connected
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / morongoa
WE USE Y-Y CONNECTION IN POWER TRANSFORMER COS WE NEED STAR
POINT SO IN DELTA YOU DNT HAVE A STAR POINT AND FOR
DISTRIBUTION YOU USE D-Y CO YOU TAKING POWER FRM SUBSTATION
WHICH IS 11KV FRM SUB TRANSFORMER TO YOUR CONSUMERS
| Is This Answer Correct ? | 1 Yes | 8 No |
what is the permissible bend in the LT& HT CABLES.
Hi Suppose we have a wye/wye transformer which is grounded at both sides,in this situation, do we have ay ground transformer? in other words, ground transformer can do any thing more (while we have nuetral wire in both sides)? As the last question, what about 3rd harmonic? we have two choices: first using wye/delta transformer + ground transformer and second using wye/wye earthed connection.in the former choice, we dont have 3rd harmoonic at the secondary side but what about Yn/yn conection? do we suffer from 3rd harmonic in the Yn/yn connection?
Magnetizing current for induction motor compared to transformer is= A equal B more C less D depends on load
why some transformer without breather.
Define what is difference between fuse and breaker?
in slip ring motor if motor specification is given how we calculate its rotor resistance in starting
HOW TO SET THE EARTH FAULT SETTINGS IN ACB????????????
WHAT is the no of starts/hr for 3.3 KV, 300 KW motor. Motor is vertical flange type.
Why Aluminium wires are used for High tension(HT) lines? 11 KVA/32KVA & aboue
Why does the DC voltage needed is less than AC needed to produce corona?
On the transformer breather at what length should i change my sililca gel.
Who is reputed manufacturer of TNC switch for ACB in India ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)