What is working principle of ACB and VCB?
Answers were Sorted based on User's Feedback
ACB: air circuit breaker./ mostly used in LT side and arc
quenching by air.
VCBL Vacuum circuit breaker. HT application. arc quenched
by vacuum.
Is This Answer Correct ? | 237 Yes | 15 No |
Answer / n karthikeyan
ACB means "AIR CIRCUIT BREAKER" it is a Electrical power
supply protection equipment when fault occur in the system.
It is used in the Low Voltage application. The power supply
mechanical contacts are kept in the atmospheric air at the
time of fault, the breaker will trip the generated electric
arc ia quenched by the air.
VCB means " VACCUM CIRCUIT BREAKER " it is also same
equipment but used in the High Voltage application ( 11kv -
33kv ), here the power supply mechanical contacts are kept
in the vaccum sealed bottle, the vaccum will quench the arc
at the time faulty trip. The electric arc generation is
high when comparing with the ACB
Is This Answer Correct ? | 88 Yes | 11 No |
Answer / annu
circuit bkrs. names related with arc quenching medium which
is used in breaker. mostly air ckt. bkr used for LT system
and arc quenching mwdium is only air but vaccume ckt. bkr.
used for HT system and arc quenching medium is vaccume
which is created in separate vaccume bottles where contacts
make and break .
Is This Answer Correct ? | 83 Yes | 14 No |
Answer / pawan ahlawat
ABB MOSTLY USED IN LT SIDE BUT VCB FOR HT SIDE
Is This Answer Correct ? | 55 Yes | 13 No |
ACB: As name it is Air circuit breaker, and it is used in
LV side of transmission, air as a arc quenching medium.
VCB: vaccume circuit breaker it used in HT side of
transmission there is not any medium for arc quenching so
it is vaccume circuit breaker
Is This Answer Correct ? | 37 Yes | 23 No |
Answer / gomez jerald
An ACB Is constructed for a particular contact rating at medium voltage .Technical explanation the contacts energize and d energize the arcing air medium during the process is quenched in an open chamber.
VCB is constructed especially for higher rating voltage and the technical term .the arcing during energizing and d energizing is quenched in closed chamber at very low pressure.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / sandesh gudekar
tungstan has high melting point than nichrome.that's why tungstan is used as filament of incandescent lamp
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / sakthi
Acb is a air circuit breaker used for Lt side arc is air qencing medium. Vcb is a vacum circuit breaker used for ht side vacum is quvancing medium
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jayprakash gupta
Vcb (vacuum circuit breaker) use of ht site
Acb (Air circuit breaker) use of lt site
Is This Answer Correct ? | 0 Yes | 0 No |
tell me about vfd
If a line which is drawing approximatly 2100amps what should be earthing streep size(using galwanize streep)?
Why neutral grounding Transformer provided for generator?
what percent do you derate your copper wire when you change from copper buss to copper wire
in india why we not use frequency above 50 hz for distrubuting power ?
How to select Main CB Rating for 220 KW Load?
I WOULD LIKE NOW WHY WE CANT USE SOME CT FOR MESARING AND PROTECTION
What are all the points to be checked for a newly re-winded motor before installation
why vacuume circuit breaker is not used for EHV
3 Answers College School Exams Tests, Crompton Greaves,
A 200W,230V lamp is connected across 115V supply.The lamp will draw power?
do we convert single phase line to three phase at minimum cost?
why m and c are shorted in wattmeter