We have a 33/11kv switchyard having 12.5 MVA power
transformer. We export & import power through this
transformer. When we export power, the PF will be depend on
GRID PF & when we import power the PF will be depend on our
load PF. but the problem is that,when neither we export nor
import but our 33KV vCB is in close position,our meter read
the power factor 0.14 to 0.25 at that moment. So how can be
we improve the power factor at that moment.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
You should realise that when there is no load on
transformer, the pf is almost zero
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / vinova
try to put some light load on your transformer during this
period if you you wnt to keep the pf high during this
period. it happens because under no load condition the
power fector angle is near 75 and power fector is high. it
happens because tansformer need reactive power for
energising its magnatic circuit. as the outer load is zero
during no load the internal load of transformer is
inductive.
| Is This Answer Correct ? | 2 Yes | 1 No |
are load variation in your plant? If variation for some minutes are in your plant then this problem should be created. In load time power factor was normal but on no load time power factor was abnormal, because we have maintain the power factor in on load position.At no load time capacitive power has make a leading power factor.for detail pl. cont. to Ab. Khalil 9977278622
| Is This Answer Correct ? | 1 Yes | 0 No |
how squirrel cage & slip ring motor works? how they differ from each other
I want single line diagram for AMF & DG syncronizing panel
what would the resistance of a 110v 150w submersiblepump motor windings be
if we have a power factor 0.99 and we add a capacitive bank with it then what happen?
If we say that an cable of size 3.5X 50 mm sq. can take current upto 140 amps,is it the current of single core of the cable or of all the cores jointly.
pls tell me about ups internal connection & we have given only 3 phase supply to ups system how get 4 wire (R Y B N )
whatis knee point ?
what is the best method of grounding in 30 MW generator?
Which is remain unchanged in transformer action?
substation+ plc system
In Indian Railways , how the AC motor is driven? Please explain clearly starting from the overhead 25kV supply.
what is the difference between current voltage transformer and current transformer and where it is used?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)