how much current we can get from 11kv overhead line ?
Answers were Sorted based on User's Feedback
It is depends on the generating station MW capacity
Is This Answer Correct ? | 19 Yes | 12 No |
Answer / prabhukumar
thats depends on the amount of load connected. depending on
that right material and protection will be used.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / a k kataria
Current to be drawn from 11kv line depends on different
factors.These factors are length of line, size of
conductor,ambient temperature of region etc.Normally 11 kv
line with Racoon conductor could carry 197 Amps and perhaps
with Dog conductor could carry 240 Amps with VD 6%.Also
Currents beyond this may create problems at breaker levls
as excessive heat coud result particularly at Joints.
Is This Answer Correct ? | 8 Yes | 5 No |
Answer / mohamed
it is depend on the type of the conductor CU or Al
it is depend on the cross section area of the Conductor
R = resistevity * length / Area
1 MM^2 ----> Cu give between 3 --> 5 Amp.
1 MM^2 -----> Al give between 1 ---> 3 Amp
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / amit
it depends upon how much load is connected and generation side production capacity
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dilip
it is depends on the rating of distribution transformer,e.g
if there is 100 kva, then it will take 5.25amp.
Is This Answer Correct ? | 12 Yes | 14 No |
Answer / mahdi
this depend on headway , capacity of line , heavay of wagon
and dever of rail , capacity of traction motor ...
electrical_powerstation@yahoo.com
expert of OCS in mashhad iran
www.murco.ir
Is This Answer Correct ? | 1 Yes | 8 No |
how wecalculate breaking capcity of acb mcb mccb .explain with example
why a three phase induction motor cannot run at synchronous speed ?
WHATS THE DIFFERENCE IN USING THE 125% AND THE 250% FACTOR OF SAFETY IN CALCULATING CIRCUIT BREAKERS CAPACITY IN MOTOR APPLICATION??
What is the difference between KV,KVAR,KVA,KW?
6 Answers L&T, PowerHouse, YUI,
my company total load is 1000kw, 415volt, all load are inductive load. incoming powerfactor is .8. we want to have0.95 pf connecting capacitors. so now how much rating of capacitors we have to connect? show how?
For maintenance Department What type documention requir for ISo & TS audit
1 Answers Megatron Solutions, Sams,
Earth has zero potential then what would be the neutral potential ?
Q. calculate the value of the resistor to be connected in series with a 100W; 230V lamp so that the wattage of the lamp is reduced to 35W
why voltage ratings of xmission are in 11, 33,66kv and why not 11.5 ,16,19 or any other
WHAT IS MEANT BY DERATING OF THYRISTOR?
Why should we use Star-Delta connection in step down power transformers?
What is LOP Sensor in DG??????