how to calclate fault level
Answers were Sorted based on User's Feedback
Answer / abhishek goyal
Its related to short circuit current because of that when we
design any plant and there electrical system. design
engg.(first calculate the total load)calculate the max SC
current according to that equipment will be select. Its
called the fault level:
it divided into 2 (Major):
low fault level (for normal equipment)
high fault level (for critical equipment)
as per total load of plant or capacity.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sakthivel
in our electrical system no of fault available there are
1,open circuits 2,short circuits 3,loose connections 4,earth
faults if any fault depends on voltage and full load current
and insulation cable so that is not idea,
Is This Answer Correct ? | 1 Yes | 1 No |
which motor is used in electric train...???????
what is compatible kva for 3300 watts and why
HOW TO CALCULATE THE APFC Panel Design
wil a dc motor run without a starter??
What is a formula to decide the size of the cable of the star delta motor ( From Contactor to the motor 2 runs )
DG use Rating KVA why
Whats the principle of lightning? How protection against lightning is achieved? Types of protection? How to select the height of lightning spike? as per the area.
how to maintain ht line?
how manyunits consumed by 25 kvar capacitor bank
what would the resistance of a 110v 150w submersiblepump motor windings be
why occ characteristics curve in not tracing back when we are bringing back the rhoestat?
in 11kv/400v transformer when only one phase of 11kv supply fails what happens to sec voltage and why